It goes on to state that the number of non-residential sprinklers can not be
greater than 4 in an entire dwelling unit, not just a compartment.    If you
can't keep the number of non-residential sprinklers to less than 4 in your
dwelling units, you seem to fall out of 13R criteria.


Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign 
LinkedIn: https://www.linkedin.com/in/travismack

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Anthony Carrizosa
Sent: Tuesday, February 13, 2018 9:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Sprinklerforum Digest, Vol 59, Issue 4

NFPA 13R does allow non residential sprinklers in dwelling units,
6.2.1.1 Listed residential sprinklers shall be used unless another type is
permitted by 6.2.1.3 or 6.2.1.4.
See 6.2.1.3-6.2.1.4 "Listed quick response sprinklers shall be permitted in
Dwelling units"

Also NFPA 13 says "residential sprinklers are permitted to be used in
dwelling units" not necessarily required in NFPA 13 designed systems.

Anthony Carrizosa
OFFICE: 253-872-7222 
Cell:         206-679-5283

Fire Protection Division 



-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of sprinklerforum-requ...@lists.firesprinkler.org
Sent: Thursday, February 08, 2018 9:21 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Sprinklerforum Digest, Vol 59, Issue 4

Send Sprinklerforum mailing list submissions to
        sprinklerforum@lists.firesprinkler.org

To subscribe or unsubscribe via the World Wide Web, visit
        
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

or, via email, send a message with subject or body 'help' to
        sprinklerforum-requ...@lists.firesprinkler.org

You can reach the person managing the list at
        sprinklerforum-ow...@lists.firesprinkler.org

When replying, please edit your Subject line so it is more specific than
"Re: Contents of Sprinklerforum digest..."

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to