The door is part of the assembly but, I just found out this is the area
where they were intending to Std Spray in lieu of WS. 

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Craig/GVL
Sent: Tuesday, February 13, 2018 3:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Glazing Protection with standard spray

 

There isn't any prescribed protection for door glazing.  There is a window
sprinkler, I think it was by Tyco that when installed per its listing was
considered equivalent to 2-hour protection but that was for fixed glazing
and with some restrictions.

 

Is this door part of a fire rated assembly or area separation?

 


Craig L. Prahl 
Fire Protection Group Lead/SME
Direct - 864.920.7540

Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
 <http://www.jacobs.com/> http://www.jacobs.com

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jerry Van Kolken
Sent: Tuesday, February 13, 2018 5:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Glazing Protection with standard spray [EXTERNAL]

 

Okay, Is been about a decade since I've dealt glazing protection. Is there
any information on protecting window with standard spray sprinklers. I've
been told this was direction was approved by the AHJ.

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722