Not sure if this will help you in anyway, but what about section D.1.1.1.1 in 
NFPA 13.

Mike Stossel SET
[400dpiLogoCropped]
36 Barren Road
East Stroudsburg, PA 18302
Office: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jerry Van Kolken
Sent: Tuesday, February 13, 2018 6:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Glazing Protection with standard spray

The door is part of the assembly but, I just found out this is the area where 
they were intending to Std Spray in lieu of WS.

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Prahl, Craig/GVL
Sent: Tuesday, February 13, 2018 3:06 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Glazing Protection with standard spray

There isn't any prescribed protection for door glazing.  There is a window 
sprinkler, I think it was by Tyco that when installed per its listing was 
considered equivalent to 2-hour protection but that was for fixed glazing and 
with some restrictions.

Is this door part of a fire rated assembly or area separation?


Craig L. Prahl
Fire Protection Group Lead/SME
Direct - 864.920.7540
Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com<mailto:craig.pr...@ch2m.com>
http://www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jerry Van Kolken
Sent: Tuesday, February 13, 2018 5:58 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Glazing Protection with standard spray [EXTERNAL]

Okay, Is been about a decade since I've dealt glazing protection. Is there any 
information on protecting window with standard spray sprinklers. I've been told 
this was direction was approved by the AHJ.