We have always addressed this under an alternative solution as the glazing
and doors are normally in a rated assembly and as such an alternative
solution was required by the architect and provided by a fire protection
engineer or code consultant.

 

We would have WS on the glazing and QR pendants over the doors with baffles
between the SSP and WS

 

 

 

Thank you

 

 

James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  jcrawf...@phaserfire.ca

Web www.phaserfire.ca

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mike Stossel
Sent: Tuesday, February 13, 2018 3:17 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Glazing Protection with standard spray

 

Not sure if this will help you in anyway, but what about section D.1.1.1.1
in NFPA 13.  

 

Mike Stossel SET

400dpiLogoCropped

36 Barren Road

East Stroudsburg, PA 18302

Office: 973-670-2627

 <mailto:m...@knssprinkler.com> m...@knssprinkler.com

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jerry Van Kolken
Sent: Tuesday, February 13, 2018 6:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Glazing Protection with standard spray

 

The door is part of the assembly but, I just found out this is the area
where they were intending to Std Spray in lieu of WS. 

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Prahl, Craig/GVL
Sent: Tuesday, February 13, 2018 3:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Glazing Protection with standard spray

 

There isn't any prescribed protection for door glazing.  There is a window
sprinkler, I think it was by Tyco that when installed per its listing was
considered equivalent to 2-hour protection but that was for fixed glazing
and with some restrictions.

 

Is this door part of a fire rated assembly or area separation?

 


Craig L. Prahl 
Fire Protection Group Lead/SME
Direct - 864.920.7540

Fax - 864.920.7129
Direct Extension  77540
CH2M is now Jacobs.
200 Verdae Blvd.
Greenville, SC  29607
craig.pr...@ch2m.com
 <http://www.jacobs.com/> http://www.jacobs.com

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Jerry Van Kolken
Sent: Tuesday, February 13, 2018 5:58 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Glazing Protection with standard spray [EXTERNAL]

 

Okay, Is been about a decade since I've dealt glazing protection. Is there
any information on protecting window with standard spray sprinklers. I've
been told this was direction was approved by the AHJ.

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722