It is a medical lab so portions are definitely light hazard but areas that are 
using and storing the flammable liquids would be OH2 IMO.


Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fpdcdesign
Sent: Wednesday, February 14, 2018 10:04 AM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: Re: Flammable and Combustible Liquid Storage

What is the surrounding occupancy?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-553-3553<tel:860-553-3553> (fax)
860-608-4559<tel:860-608-4559> (cell)



On Feb 14, 2018 at 10:50 AM, <Matt Grise<mailto:m...@afpsprink.com>> wrote:

I think that NFPA 30 hits on general sprinkler protection. It has been a while 
since I was in that book, but I seem to recall that OH2 is about right.



Matt





-----Original Message-----

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Reed A. Roisum, SET

Sent: Wednesday, February 14, 2018 9:39 AM

To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>

Subject: Flammable and Combustible Liquid Storage



IFC 2012 Table 5003.1.1 gives the maximum allowable quantities of flammable and 
combustible liquids per control area.  If the liquids are stored in approved 
cabinets you can increase the volume by 100%.



I am trying to determine the proper sprinkler design for areas that contain 
flammable and combustible liquids that are stored in approved cabinets.  NFPA 
13, 2010 edition states that occupancies with moderate to substantial amounts 
of flammable or combustible liquids shall be designed to Extra Hazard Group 2 
(5.4.2).  However, I am confident that because the liquids are in cabinets that 
this space would not be designed to EH2, but I can't find any verbiage that 
explicitly says so.  I believe Ordinary Hazard Group 2 is adequate but I need 
to document from the codes and standards my reasoning.



Can anyone point me to a code or standard section that states that if flammable 
or combustible liquids are stored in approved cabinets that you basically don't 
have to account for their presence?...at least I believe that is the intent so 
please correct me if I am wrong.



Thank you.



Reed Roisum





Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
http://www.kfiengineers.com





______________________________________________________________________

This email has been scanned by the Symantec Email Security.cloud service.

For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to