I’m so used to seeing everything being CL 52 cement lined DIP I have to ask. Is 
DIP that isn’t cement lined readily available?

Do you need to use a C-factor in design that accounts for future corrosion with 
unlined DIP? 

Best.

Bruce Verhei 

> On Feb 19, 2018, at 10:18, Reed A. Roisum, SET <raroi...@kfi-eng.com> wrote:
> 
> Correct.
> 
> 
> Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
> Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Prahl, Craig/GVL
> Sent: Monday, February 19, 2018 11:58 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Underground Dry System Pipe Type
> 
> Using nitrogen should help mitigate the corrosion issue with standard DI.
> 
> I assume there will be a drum-drip back in the riser room so they can keep 
> the line drained?
> 
> 
> Craig L. Prahl
> Fire Protection Group Lead/SME
> Direct - 864.920.7540
> Fax - 864.920.7129
> Direct Extension  77540
> CH2M is now Jacobs.
> 200 Verdae Blvd.
> Greenville, SC  29607
> craig.pr...@ch2m.com
> http://www.jacobs.com
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Reed A. Roisum, SET
> Sent: Monday, February 19, 2018 12:51 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Underground Dry System Pipe Type [EXTERNAL]
> 
> Thanks Craig.  Yes, the valve room is below grade.
> 
> If we use nitrogen to charge the dry system then would we just use standard 
> DI?
> 
> 
> Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
> Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Prahl, Craig/GVL
> Sent: Monday, February 19, 2018 11:36 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: Underground Dry System Pipe Type
> 
> Cement lined ductile iron.  If you use standard DI, and a standard 
> atmospheric sourced air compressor you can have rust and scaling buildup with 
> ambient air inside pipe in contact with cooler ground temps.
> 
> How are you going to slope underground pipe back to an aboveground valve 
> room?  Basement level valve room?
> 
> 
> Craig L. Prahl
> Fire Protection Group Lead/SME
> Direct - 864.920.7540
> Fax - 864.920.7129
> Direct Extension  77540
> CH2M is now Jacobs.
> 200 Verdae Blvd.
> Greenville, SC  29607
> craig.pr...@ch2m.com
> http://www.jacobs.com
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Reed A. Roisum, SET
> Sent: Monday, February 19, 2018 12:11 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Underground Dry System Pipe Type [EXTERNAL]
> 
> I asked a similar question a number of years ago and it appears as though the 
> consensus at that time was that dry-pipe system underground pipe should be 
> ductile iron.  We have an application where the dry-pipe system leaves the 
> valve room and goes underground and then extends above ground.  Is ductile 
> iron the best option for the underground portion?  We are able to slope to 
> drain back to the valve room.
> 
> Thank you.
> 
> Reed Roisum
> 
> 
> Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
> Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
> KFIengineers.com<http://www.kfiengineers.com>
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180219/ab1fd556/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to