My bad. There was a typo in my original message.  I was trying to refer to 
A.31.3.3.2.2,  but I dropped the first "3".

Here is what A.31.3.3.2.2 from the 2018 edition says:

A.31.3.3.2.2   It is recognized that retail and wholesale lumber storage yards 
are normally located within municipal system boundaries, where the system 
should be capable of supplying not less than four 21⁄2 in. (65 mm) hose streams 
simultaneously [1000 gpm (4000 L/min)]. Where large-scale firefighting 
operations can be expected, larger water supplies are needed. Where protection 
from municipal water supplies and hydrant systems is not provided or is not 
considered adequate by the AHJ, a yard fire hydrant system should be provided 
and installed in accordance with NFPA 24.

Larry


-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-23-18 10:38 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

I'm sorry Larry, not following.  Those section numbers not found in the Annex 
of 2015 edition either.

SL

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Friday, February 23, 2018 7:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

I was citing the NFPA 1 - 2015 edition.

Larry

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-22-18 5:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

Which edition are you citing?  2018 doesn't have those Annex sections.

SL

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Larry Keeping
Sent: Thursday, February 22, 2018 2:37 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Lumberyard fire flows

[This message was identified as a phishing scam. Learn about phishing at 
http://aka.ms/LearnAboutPhishing]

NFPA 1 in A.1.3.3.2.2 and A.3.4.3.1 provides some guidance regarding flow and 
hydrant spacing for outside storage such as you are dealing with.

Best regards,

Larry Keeping

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: February-22-18 1:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Lumberyard fire flows

This isn't a sprinkler question specifically, but FP-related:   Has anyone ever 
worked on design of a private fire main for a lumberyard?   Huge outdoor piles 
of stored wood products, engineered members mostly, some smaller amounts of 
dimensional lumber.     We're trying to establish a fire flow for hydrants but 
there are no buildings of any size to benchmark and tables in the fire code are 
not of much use because they're based on building area and construction type.   
The fire load here is not in buildings ...

[Steve Signature (3)]

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 23565 bytes
Desc: image003.png
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180222/e44a9d59/attachment.png>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list