It is in every section in the storage sprinklers (CMDA, CMSA, ESFR).

Check 16.2.1.4.3.1 of the 2016 edition for an example.  The handbook
completely clarifies the issue.

"The user must add the water demand for the designated number of in-rack
sprinklers for the specific 
design application from 16.2.1.4.3.1 to the demand calculations for the
ceiling sprinklers and balance to 
the higher of the two pressure demands to ensure that the water supply can
handle the simultaneous 
operation of ceiling and in-rack sprinklers."


Travis Mack, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign 
LinkedIn: https://www.linkedin.com/in/travismack

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Easter, Timothy M CIV NAVFAC MIDLANT, CI
Sent: Friday, February 23, 2018 11:30 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: inrack sprinkler question

Does the in-rack sprinkler system need to be combined with the ceiling
sprinkler system, for hydraulic calcs? Can anyone cite reference that
requires this?

V/R,
Timothy M. Easter, P.E.
NAVFAC Mid-Atlantic
Capital Improvements 
Fire Protection Engineer 
Comm: (757) 341 - 0130 / DSN 341 - 0130
Office Hours: 0800 - 1730
RDO: 2nd Friday


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to