I am not sure. In that case. there is no design criteria given for the HE
foam system. Any thoughts?

Tony

On Fri, Feb 23, 2018 at 2:27 PM, Art Tiroly <atir...@atcofirepro.com> wrote:

> I believe that means a HE foam system plus a sprinkler system with a .30
> density.
>
>
> Art Tiroly
> ATCO Fire Protection
> 24400 Highland Rd CLE 44143
> 216-621-8899
> 216-570-7030 cell
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org]
> On Behalf Of Tony Silva
> Sent: Friday, February 23, 2018 3:39 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Tire Storage
>
> NFPA 13, 2014 Table 18.4(a)
>
> Some "Sprinkler Discharge Densities" are given as (for example):
>
> "0.30 plus high expansion foam"
>
> Does this mean the roof system needs to be high expansion foam with a
> density of 0.3? I'm just confused with the use of the word "plus" and want
> to make sure it doesn't mean anything else.
>
> Thanks,
>
> Tony
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.
> org
> /attachments/20180223/131521aa/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
> ---
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180223/dbb5aad0/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org