Craig,

Thank you for the reply. I appreciate your frequent contributions to the forum, 
and I agree with your interpretation of the spacing rules. With respect to the 
head spacing on different lines, I am not going to second guess the designer. 
This is a large industrial type project with a significant amount of utilities, 
piping, cable trays, etc., as well as interior partitions. As he is employed 
directly by the sprinkler contractor that is installing this system, I am 
confident that he chose the most economical arrangement to satisfy the many 
constraints of this installation.

At the sprinkler contractor’s request, I did send a virtually identical 
question as an informal interpretation through NFPA last Friday. I will share 
that response when I receive it.

Have a great (and profitable) day!

Sent from my iPad

Christopher H. Born, P.E.
Director, Fire Protection Engineering|Principal
Clark Nexsen
4525 Main Street, Suite 1400
Virginia Beach, VA 23462
(757) 455-5800
(757) 961-7933 (direct)
(757) 644-8581(mobile)

> On Mar 12, 2018, at 8:30 AM, Prahl, Craig/GVL <craig.pr...@ch2m.com> wrote:
> 
> When a perpendicular obstruction becomes deep enough that the sprinkler 
> discharge is cannot throw under it based on the obstruction rules set forth 
> in NFPA 13, then you treat it the same as if it was a wall and space the 
> branch lines accordingly.  If I have a steel framed building with 20 ft bays 
> and at the column lines there are 36" deep beams
> 
> It's really very simple.  Look at the distance of the deflector below the 
> deck and the distance above the bottom of the obstruction as well as the 
> distance off the edge of the obstruction in Chapter 8 of NFPA 13.
> 
> Also, why would your designer add additional sprinklers to a branch line?  
> Where is the justification or direction for this coming from?  
> 
> If you have an obstruction, you just space the branch lines differently to 
> accomplish a uniform spacing arrangement in the bay or area where the 
> obstruction occurs.
> 
> 
> Craig L. Prahl 
> Fire Protection Group Lead/SME
> Direct - 864.920.7540
> Fax - 864.920.7129
> Direct Extension  77540
> CH2M is now Jacobs.
> 200 Verdae Blvd.
> Greenville, SC  29607
> craig.pr...@ch2m.com
> http://www.jacobs.com
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of Chris Born
> Sent: Thursday, March 08, 2018 11:54 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Protection Area of Coverage for Sprinkler [EXTERNAL]
> 
> 8.5.2.1.1 of the 2016 edition of NFPA 13 covers how to determine the area 
> covered by a sprinkler. This seems to be pretty straightforward, but I’ve 
> noticed some strange wording. Consider a building with exposed structure and 
> some beams that are deep enough to be obstructions, 36” as an one example.
> 
> For spacing between branch lines, the standard says “Determine perpendicular 
> distance to the sprinkler on the adjacent branch line (or to a wall or 
> obstruction in the case of the last branch line) ...” I understand the 
> reference to last branch line when referring to a wall, but not with respect 
> to an obstruction. Similar language exists for spacing along the line. 
> 
> Is this just poor wording, or is it really the intent not to allow 
> measurement to an obstruction if not the end line or sprinkler? I have a case 
> where a deep beam requires an additional line.  The designer has spaced heads 
> closer together on the line that is further from the beam, so calculating 
> head spacing times twice the distance to the beam results in an area of less 
> than 100 sq ft (this is extra hazard). However, if the intent is to use the 
> distance to the next line (and ignore the beam) then the area is over 100 sq 
> ft. I think the layout meets the intent, but am interested in other opinions.
> 
> Sent from my iPad
> 
> Christopher H. Born, P.E.
> Director, Fire Protection Engineering|Principal Clark Nexsen
> 4525 Main Street, Suite 1400
> Virginia Beach, VA 23462
> (757) 455-5800
> (757) 961-7933 (direct)
> (757) 644-8581(mobile)
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: 
> <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180308/c689782f/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180312/aa0b8d4f/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to