There are some of these ducts that have internal struts/ribs that hold the duct open even when air is off, others do not have the internal support and will go limp if HVAC is shut down.
So, if there were a sprinkler below the duct and fire broke out fusing that sprinkler, and if the HVAC system is interlocked to shut down on sprinkler flow, the HVAC system shuts down, duct collapses and sprinkler is rendered inoperable. You will need to verify the type of duct that is being provided and HVAC interlocks which may require another conversation with the insurer. Craig L. Prahl Fire Protection Group Lead/SME Direct - 864.920.7540 Fax - 864.920.7129 Direct Extension 77540 CH2M is now Jacobs. 200 Verdae Blvd. Greenville, SC 29607 craig.pr...@ch2m.com http://www.jacobs.com -----Original Message----- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Phillips, Mark Sent: Tuesday, March 13, 2018 1:29 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Duct Sox / ESFR [EXTERNAL] The underwriter insisted that we treat it as a fixed duct because that was the worst case scenario Mark Phillips Vice President of Fire Protection, Kirlin Carolinas, LLC t: 919-526-1584 mphill...@jjkllc.com | https://kirlingroup.com Raleigh, NC 27617 -----Original Message----- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Tuesday, March 13, 2018 1:19 PM To: sprinklerforum@lists.firesprinkler.org Subject: Duct Sox / ESFR Has anyone come across the duct sox and ESFR protection? How do you handle these? I intend to put a sprinkler under the duct as normally required. But, these somewhat vanish when the HVAC system is off. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:tm...@mfpdesign.com> email:tm...@mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4 2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2 FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b 4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166 77342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C 14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2 wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0> https://www.hightail.com/u/MFPDesign LinkedIn: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77% 7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0> https://www.linkedin.com/in/travismack "The bitterness of poor quality remains long after the sweetness of low price is forgotten." -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/cbbc7280/attachment.html> -------------- next part -------------- A non-text attachment was scrubbed... Name: image001.jpg Type: image/jpeg Size: 6420 bytes Desc: not available URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/cbbc7280/attachment.jpg> _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/4082552d/attachment.html> -------------- next part -------------- A non-text attachment was scrubbed... Name: image449421.png Type: image/png Size: 21698 bytes Desc: image449421.png URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/4082552d/attachment.png> -------------- next part -------------- A non-text attachment was scrubbed... Name: image169335.png Type: image/png Size: 501 bytes Desc: image169335.png URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/4082552d/attachment-0001.png> -------------- next part -------------- A non-text attachment was scrubbed... Name: image836894.png Type: image/png Size: 414 bytes Desc: image836894.png URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/4082552d/attachment-0002.png> -------------- next part -------------- A non-text attachment was scrubbed... Name: image815397.png Type: image/png Size: 422 bytes Desc: image815397.png URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180313/4082552d/attachment-0003.png> _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org