If the system was previously able to provide OH2, is it a problem to have over 
discharge? Could you make sure all of the heads are QR and just have a light 
hazard system with lots of extra water?

Matt 


From: Sprinklerforum <[email protected]> On Behalf 
Of Dewayne Martinez
Sent: Thursday, March 15, 2018 5:42 PM
To: [email protected]
Cc: Dewayne Martinez <[email protected]>
Subject: Existing 3/4" outlets

I have a project that was originally designed as a OH II space that will now be 
turned into a light hazard residential exposed “loft” space.  The existing ¾” 
K8.0 sprinklers over discharge like crazy.  Can I bush the 3/4'” outlets down 
to ½” to use K5.6 sprinklers?  If not any suggestions?



Dewayne Martinez

Fire Protection Design Manager



*TOTAL* *Mechanical*

*Building* *Integrity*


W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected]

Ph:  262-522-7110

Cell: 414-406-5208

http://www.total-mechanical.com/

[image: Consecutive Honors 2012-2017]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/41e14879/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 8202 bytes
Desc: not available
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180315/41e14879/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to