Brad -

I'd eat a case of aspirin to do that!

I like Mark's idea too. I'm going to look inside the pipe, via a coupon or just to cut it. I don't think there'll be a problem on the vertical stuff, more than likely on
the horizontal.

If it looks bad anywhere, I'll set up a flow test, discharging a known amount of water through a known distance of the old pipe. I'll enter that info into 'The' (hydraulic program)
and mess with the C value until the results are duplicated.

The engineer increased the pressure rating of the pump so I could probably push the
requirement through a swizzle stick anyway.

Thanks, Mark & Brad!


On 3/21/2018 3:02 PM, [email protected] wrote:
The lab would not even need a biologist on staff Vince!
They couldn't tell you what the C Factor was, but if they could measure the absolute roughness you could take it from there. I like Mark's idea of a mechanical tee coupon - send them that and they can measure the height/depth of the inside wall 'irregularities'. Say that comes up .0059 inches- that means moderately coroded- Absolute Roughness- that's all they could tell you. Since the same height on 2" affects the flow of the same height on 6" far more, you have to calculate the Relative Roughness. Then, if I was you, I would use the Swamee Jain equation for solving for the friction factor, look at NFPA 750 and rearange the formula that solves the friction factor based on C and solve for C based on the friction factor instead.
Brad

Quoting "Mark.Phelps" <[email protected]>:

My experience with old wet standpipes is that they are almost always in very good shape internally. A quick proof is to drill a hole for a 2" mech tee and check the coupon for wall thickness and interior condition.

Mark at Aero
602 820-7894

Sent from my iPhone

On Mar 21, 2018, at 3:21 AM, Vince Sabolik <[email protected]> wrote:

Forum -

I was wondering if anyone has had occasion  to have a lab test piping to establish a C value. I know that we could back into this value through a point to point flow test, but would
rather have it tested for.

If you have had experience with a lab, can you forward their name and requirements?

I working in an old building (80 yrs ±) and want to reuse the old wet standpipes.

thanks, Vince


11351 Pearl Road /  Suite 101
Strongsville, Ohio 44136
Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601

/
Vince Sabolik /

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_private.cgi_sprinklerforum-2Dfiresprinkler.org_attachments_20180321_a7c32be4_attachment.html&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=wonrpay3YRA9EUKSZyCiNhdFxfndtvADSfHaW35jg4c&s=G8i8243QOojHH4pgTwLldLTMRabS_edRfJDO1vmSFlE&e=>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 20914 x WTFP Logo NEW1.jpg
Type: image/jpeg
Size: 30521 bytes
Desc: not available
URL: <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_private.cgi_sprinklerforum-2Dfiresprinkler.org_attachments_20180321_a7c32be4_attachment.jpg&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=wonrpay3YRA9EUKSZyCiNhdFxfndtvADSfHaW35jg4c&s=WsuSS1w1LmDEsShOv7wW_-He2ibGH5gbROXfnmAQElQ&e=>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=wonrpay3YRA9EUKSZyCiNhdFxfndtvADSfHaW35jg4c&s=dtl4X4fGBtyOiiptraoXk0jsAXCLVhAAs81q3UlBzMM&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--


*Vince Sabolik*

*West Tech Fire Protection, Inc.***

11351 Pearl Road   /   Strongsville, Ohio   44136

Phone 440 238-4800    Fax 440 238-4876   Cell 440 724-7601

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180321/56e6daa9/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: gfeljhibhmdojhma.bmp
Type: image/bmp
Size: 64734 bytes
Desc: not available
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180321/56e6daa9/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to