I’ve done them many times and the pressures are the same.
It’s done by throttling the individual valves.  It takes time and patience but 
it can be done.  


Regards,Sean Conlin

On Thursday, March 29, 2018, 2:22 PM, Hinson, Ryan <[email protected]> wrote:

#yiv7784289223 #yiv7784289223 -- _filtered #yiv7784289223 {panose-1:2 4 5 3 5 4 
6 3 2 4;} _filtered #yiv7784289223 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 
3 2 4;}#yiv7784289223 #yiv7784289223 p.yiv7784289223MsoNormal, #yiv7784289223 
li.yiv7784289223MsoNormal, #yiv7784289223 div.yiv7784289223MsoNormal 
{margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:sans-serif;}#yiv7784289223
 a:link, #yiv7784289223 span.yiv7784289223MsoHyperlink 
{color:#0563C1;text-decoration:underline;}#yiv7784289223 a:visited, 
#yiv7784289223 span.yiv7784289223MsoHyperlinkFollowed 
{color:#954F72;text-decoration:underline;}#yiv7784289223 
p.yiv7784289223msonormal0, #yiv7784289223 li.yiv7784289223msonormal0, 
#yiv7784289223 div.yiv7784289223msonormal0 
{margin-right:0in;margin-left:0in;font-size:11.0pt;font-family:sans-serif;}#yiv7784289223
 span.yiv7784289223EmailStyle18 
{font-family:sans-serif;color:windowtext;}#yiv7784289223 
.yiv7784289223MsoChpDefault {font-family:sans-serif;} _filtered #yiv7784289223 
{margin:1.0in 1.0in 1.0in 1.0in;}#yiv7784289223 div.yiv7784289223WordSection1 
{}#yiv7784289223 
I’ve never seen them all identical.
 
  
 
Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
 
Senior Fire Protection Engineer
 
O 952-656-3662 \ M 320-250-5404  \ F 952-229-2923
 
[email protected]  \ burnsmcd.com
 
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
 
*Registered in: LA, MD, MN, PA, TX, & UT
 
**NICET IV - Water-Based Systems Layout
 
  
 
From: Sprinklerforum <[email protected]>On Behalf 
Of Tom Wellen
Sent: Thursday, March 29, 2018 1:15 PM
To: [email protected]
Subject: Playpipe Pitot Pressures - Fire Pump Annual Tests
 
  
 
  
 
In my insurance days, I seldom had the same pitot pressures from playpipes. The 
pressures would be the same on several but others would be 1 to 2 psi different.
 
  
 
I'm seeing fire pump reports consistently showing all the same pitot pressures 
for all four to six playpipes. I'm questioning that based on my past 
experience. Is the same pressures on pitots that common?
 
  
 
  
 
Tom Wellen 
 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to