I checked with a few others on the NFPA 11 committee who regularly do 
inspections and we all agreed this form is suitable for Medium and High 
Expansion foam, as well. It should be relabeled as such. NFPA 11 will be open 
for comments in January of 2018 so I will submit the change then.

Thanks for bringing this to the attention of the NFPA 11 committee.

Joan Leedy
Dyne Fire Protection Labs
2357 Ventura Drive, Suite 108
Woodbury, MN 55125
800-632-2304
651-917-0644
www.dyneusa.com

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jerry Van Kolken
Sent: Tuesday, March 27, 2018 2:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Contractor's Material and Test Cert from NFPA 11




The Contractor's Material and Test Certificate for in NFPA is labeled 
"Low-Expansion" Foam, is this form intended for Medium and High Expansion as 
well?


Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730