Are the aisles narrow like 30-48”?

The cat walks are likely considered obstruction to the ESFR roof system.

Therefore QR sprinklers are required below the cat walks.

See Section 20.7.3. for ESFR. Does this qualify with these 10 requirements?





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Zachary Siegrist
Sent: Tuesday, April 03, 2018 4:34 PM
To: [email protected]
Subject: Special Designs of Storage Protection Section 20.5 (2013 ed.)



All,

I am an AHJ and was called to inspect a installation for protection of carton 
record storage for a single- level catwalk.  The existing ceiling level 
protection is an ESFR system.  Section 20.5.6.2.1 states that ceiling 
sprinklers spaced to cover a maximum of 100 SF shall be standard response spray 
sprinklers with K-factors per Section 12.6.  Is this explicitly stating that 
there can't be an ESFR system at the deck level (35 feet AFF) b/c of its fast 
response element?   Does Section 12.6.6 make this permissible?  Appreciate any 
feedback I can get.



Zach



---