I can appreciate your opinion, but I need a code reference.  😉


John Irwin

DynaFire Inc. – “*Same Day – Next Day*”



*From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
Behalf Of *Steve Leyton
*Sent:* Friday, April 13, 2018 1:47 PM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* RE: Exterior Play Area



Assuming there’s play equipment there (fire load) and knowing that there
are kids occupying the space, I wouldn’t call this an “exterior
projection”.   It’s a shad structure with occupancy below and IMO requires
sprinkler protection.



SML



*From:* Sprinklerforum [
mailto:sprinklerforum-boun...@lists.firesprinkler.org
<sprinklerforum-boun...@lists.firesprinkler.org>] *On Behalf Of *John Irwin
*Sent:* Friday, April 13, 2018 10:42 AM
*To:* sprinklerforum@lists.firesprinkler.org
*Subject:* Exterior Play Area



Protecting a light hazard Boys and Girls Club. I excluded an exterior, but
covered, attached and open play area. Non-combustible. It’s a couple
thousand square feet. I excluded using NFPA 13 2013 8.15.7



Client is telling me that he her other fire sprinkler guys telling him he
needs sprinklers in that areas.



What say you?







John Irwin

Fire Sprinkler Specialist

DynaFire, Inc. – “*Same Day – Next Day*”

727-282-9243 – Cell



*“A customer is the most important visitor on our premises. He is not
dependent on us. We are dependent on him. He is not an interruption on our
work. He is the purpose of it. He is not an outsider on our business. He is
a part of it. We are not doing him a favour by serving him. He is doing us
a favour by giving us an opportunity to do so.”*
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to