No one could or would in their right mind write a letter guaranteeing the 
performance of anything.  There are far too many variables and an AHJ with any 
experience should know that.
The best anyone could do would be to state that the product is expected to 
perform as tested by the mfgr when installed and maintained according to its 
listing and conditions, water supply and pressures are as calculated and 
expected.
Good Luck!

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | 
[email protected] | www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of John Paulsen
Sent: Wednesday, April 25, 2018 12:02 PM
To: [email protected]
Subject: [EXTERNAL] Egress Window Protection

Good Day Fellow Forumites!

I have been trying to deal with a local code authority with regard to an 
"alternative" use for automatic sprinklers and I have run up against an 
obstacle that I would like to get the forum's opinion on what approaches or 
methods can be used to satisfy the plan reviewer.
The Situation:
We are dealing with an existing 4 story inner city apartment renovation. The 
building has been gutted and refurbished into a new residential (R-2) 
occupancy. The building is protected by a new 13R sprinkler system supplied by 
municipal water. Pretty much standard up to this point.
The building has an exterior fire escape structure that utilizes the existing 
double hung windows as points of egress from the apartments. These windows are 
protected by individual sprinklers mounted at the center of each window with 
the deflector no more than 2" above the window opening. These K 5.6 heads are 
calculated to flow 20 GPM at 15 PSI. The thought process behind this is that 
the sprinkler, when activated, will protect the window glass and preserve the 
path of egress for the tenants trying to leave the structure.
We have designed several of these projects over the last two years and I have a 
standard detail block that I put on each drawing that shows the spray pattern 
of the sprinkler, mounting detail, a letter from the manufacturer's PE 
detailing the test procedure that was used to determine the sprinkler spray 
pattern and a reference to NFPA-13, 2016, Section 23.3.7.1.
This detail has satisfied the plan reviewers for months, but now they a 
requiring a letter from an FPE (YES, not a PE) or the manufacturer saying the 
sprinkler will "provide 100% wetting of the glazing surface". As you can 
imagine, in our law suite happy land, the manufacturer is reluctant to write 
this letter and I don't know any FPE's that I can ask to write such a letter or 
if they would laugh me off the phone if I did.
Has anyone else dealt with this type of issue and if so, HOW!?
Thanks,
John Paulsen - SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P - 614-782-2438
F - 614-782-2374
C - 614-348-8206



________________________________________________________________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to