I get it now. The building has two egress stairwells as Steve put it. That 
offset portion is going to be no-man’s land for all disciplines to cross and 
possibly you also. That’s something to verify with the AHJ. 

> On May 1, 2018, at 12:34 PM, Jerry Van Kolken <[email protected]> wrote:
> 
> I’m trying to figure out if I need another isolation valve or if I can save 
> about 50’-60’ of piping.
>  
> The sprinkler system if feed from a combination standpipe in the stair well 
> that runs all 12 floors.
>  
> Jerry Van Kolken
> Millennium Fire Protection
> (760) 722-2722
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of AKS-Gmail-IMAP
> Sent: Tuesday, May 01, 2018 9:14 AM
> To: [email protected]
> Subject: Re: Secondary Standpipe on Upper Levels
>  
> The reason behind these questions is because the situation does not smell 
> right and we are trying to envision how this thing works within the building 
> code. 
>  
> When you enter an egress stairwell you are supposed to be entering a 
> structure that basically guarantees a safe path to street level safety out of 
> the next doorway. The implications for this extends into how the enclosure 
> for this path is isolated from the building structure itself and all MEP 
> systems. That stairwell egress path typically commands the highest enclosure 
> protection of anything else in the building. How that super protected egress 
> path is traversing half the building on the 10th floor of a 12 story 
> high-rise is a head scratcher in many ways. 
>  
> In the very least that passage is functionally part of the lower stairwells. 
> If it actually connects to both the lower stairwells, providing an exiting 
> choice at the 10th floor, then you have the question as to whether or not one 
> or both of the lower standpipes should supply that upper stairwell standpipe. 
> It sounds like it is not the same situation as having one of the stairwells 
> being a straight shot all the way up to the 12th floor.
>  
> By the way, what supplies the floor level sprinkler systems?
>  
> Allan Seidel
> St. Louis                              
> 
> 
> On May 1, 2018, at 10:09 AM, Jerry Van Kolken <[email protected] 
> <mailto:[email protected]>> wrote:
>  
> Correct, it will be a second stair for the upper level until you get to the 
> first full floor at level 10. Then your be roughly in the middle of the floor 
> and would travel to either end of the building to the full set of stairs down 
> to the ground floor.
>  
> Jerry Van Kolken
> Millennium Fire Protection
> (760) 722-2722
>  
> From: Sprinklerforum [mailto:[email protected] 
> <mailto:[email protected]>] On Behalf Of Steve 
> Leyton
> Sent: Monday, April 30, 2018 8:25 PM
> To: [email protected] 
> <mailto:[email protected]>
> Subject: Re: Secondary Standpipe on Upper Levels
>  
> So it's an offset stair, correct? In other words, it doesn't just go from an 
> upper floor down 3 levels to a lobby, it stays in an exit passageway and you 
> go horizontally on the transfer floor to a different stairwell for the rest 
> of the trip down to exit discharge, is that right?
>  
>  
> Steve
>  
>  
> -------- Original message --------
> From: Jerry Van Kolken <[email protected] <mailto:[email protected]>>
> Date: 4/30/18 5:39 PM (GMT-08:00)
> To: [email protected] 
> <mailto:[email protected]>
> Subject: Re: Secondary Standpipe on Upper Levels
>  
> The building loses half of the floor on the upper levels, so it’s a second 
> stair for the top levels. And the ahj is calling it a required exit
> 
> Jerry Van Kolken
> 
> On Apr 30, 2018, at 16:01, Steve Leyton <[email protected] 
> <mailto:[email protected]>> wrote:
> 
>> Why is there a “partial stairwell”?    Is it classified as required exit 
>> stair or a convenience stair?   
>>  
>> Steve L.
>>  
>> From: Sprinklerforum [mailto:[email protected] 
>> <mailto:[email protected]>] On Behalf Of Jerry 
>> Van Kolken
>> Sent: Monday, April 30, 2018 3:04 PM
>> To: [email protected] 
>> <mailto:[email protected]>
>> Subject: Secondary Standpipe on Upper Levels
>>  
>> I have a 12 story project with a partial stairwell on the top 3 floors. The 
>> AHJ is requiring a standpipe at this partial stairwell. My question is to I 
>> need to run another vertical feed from the pump on the first floor, or can I 
>> do a horizontal feed off the standpipe in the opposite stairwell on the 
>> upper level?
>>  
>> Jerry Van Kolken
>> Millennium Fire Protection Corp.
>> 2950 San Luis Rey Rd.
>> Oceanside, CA 92058
>> (760) 722-2722 FX 722-2730
>>  
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected] 
>> <mailto:[email protected]>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
>> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to