Is it possible to have the unit heaters mounted more than 7 feet BELOW the sprinkler heads? That allows you to use intermediate temp heads [see Table 8.3.2.5(a)].
This has worked for us in the past. If they are mounting the unit heaters to columns, that should be feasible. This would be option 1 if it were my job. -Kyle M From: Sprinklerforum [mailto:[email protected]] On Behalf Of Don Casey Sent: Wednesday, May 2, 2018 8:27 AM To: [email protected] Subject: [EXTERNAL] RE: ESFR sprinklers near unit heaters Have you confirmed what the temps are expected to be below the unit heater? The manufacturer’s data (or the mech engineer) may be able to provide this info. Cheers Don From: Sprinklerforum [mailto:[email protected]] On Behalf Of Tony Silva Sent: 2018/05/02 11:23 AM To: [email protected]<mailto:[email protected]> Subject: Re: ESFR sprinklers near unit heaters Even if in the 7 foot unit heater zone, with the possibility of a sprinkler being activated? Would it be a lesser evil if a non-ESFR 286 deg.F sprinklers having the same k factor as the ESFR sprinklers are used only near the unit heaters with the rest of the system being ESFR? Tony On Wed, May 2, 2018 at 8:59 AM, Mike Hairfield <[email protected]<mailto:[email protected]>> wrote: Use the 212 deg. ones. ASCOA used to make a 286 deg. one but they are out of business. Mike ________________________________ From: Sprinklerforum <[email protected]<mailto:[email protected]>> on behalf of Tony Silva <[email protected]<mailto:[email protected]>> Sent: Wednesday, May 2, 2018 10:57 AM To: [email protected]<mailto:[email protected]> Subject: ESFR sprinklers near unit heaters Are there any ESFR sprinklers rated for 286 deg.F? If not, how would you locate them near unit heaters when it is next to impossible to maintain a minimum 7 feet clearance? How have others solved this problem? Tony _______________________________________________ Sprinklerforum mailing list [email protected]<mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=c68_zyNIDTI3CHr36rIBp8ceWv2euaU1ZPfykuvgM2o&s=Y8jwcLmpmXIAu6Wn-AijOP88eWhRXUsdCQiXvaneAIE&e=>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org