Here's the NEC Code Section;


2017 NEC



250.104 Bonding of Piping Systems and Exposed Structural

Metal.



(A) Metal Water Piping. The metal water piping system shall

be bonded as required in (A)(1), (A)(2), or (A)(3) of this

section.



(1) General. Metal water piping system(s) installed in or

attached to a building or structure shall be bonded to any of

the following:



(1) Service equipment enclosure

(2) Grounded conductor at the service

(3) Grounding electrode conductor if of sufficient size

(4) One or more grounding electrodes used, if the grounding

electrode conductor or bonding jumper to the

grounding electrode is of sufficient size



The bonding jumper(s) shall be installed in accordance with

250.64(A), 250.64(B), and 250.64(E). The points of attachment

of the bonding jumper(s) shall be accessible.





John Drucker, CET
Acting Construction Official
Fire and Electrical Subcode Official
Building Inspector
Building Department
Borough of Red Bank, NJ
Cell/Text 732-904-6823
________________________________
From: Sprinklerforum [[email protected]] on behalf 
of John Drucker [[email protected]]
Sent: Thursday, May 10, 2018 2:40 PM
To: [email protected]
Subject: RE: Grounding Electrical Wire to Sprinkler System


Correct cannot be used for "GROUNDING".



However per the NEC all metallic water piping including sprinkler piping is 
required to be "BONDED".



GROUNDING = Used to connect the building electrical system to Earth. Fire 
Sprinkler piping including Underground, FDC's etc are not considered ground 
electrodes by the NEC. So they cannot be used for that purpose



BONDING = To connect all metallic parts to the electrical system of the 
building such that these items cannot become energized resulting in the risk of 
electrocution  Bonding allows fault current to flow through the bonding wire 
connection thus enabling sufficient current to flow tripping the connected 
circuit breaker eliminating the hazardous condition.



Hope that helps.



John Drucker, CET
Fire and Electrical Subcode Official
Building Inspector
Building Department
Borough of Red Bank, NJ
Cell/Text 732-904-6823
________________________________
From: Sprinklerforum [[email protected]] on behalf 
of JD Gamble [[email protected]]
Sent: Thursday, May 10, 2018 2:31 PM
To: [email protected]
Subject: RE: Grounding Electrical Wire to Sprinkler System

10.5.1 2016 ed
Life Safety Solutions of Sheridan

JD Gamble
[email protected]<mailto:[email protected]>
(307) 763-3361
From: Sprinklerforum <[email protected]> On Behalf 
Of Mike Hairfield
Sent: Thursday, May 10, 2018 12:28 PM
To: Sprinkler Forum <[email protected]>
Subject: Grounding Electrical Wire to Sprinkler System

Where in NFPA 13 does it say that the sprinkler system can not be used to ground

the electrical system?



Thanks,



Mike