I bet if you dig into these specs, you'll find some safety factors: Federal Specification A-A-1192A (Type 10) WW-H-171-E (Type 10), ANSI/MSS SP-58 (Type 10). UL Listed and FM Approved (Sizes 3⁄4" - 8")
Table 9.2.2.1(a) 2” hanger every 15’ Table A.9.3.5.9 2” sch 40 5.13 lbs/ft 15’ x 5.13 = 76.95 lbs @ hanger 77 lbs x 5 = 385 lbs + 250 = 635 lbs The 300 lb or 400 lb rating on hanger spec sheets is Low Number and the Tested weight is divided by a safety factor. Chuck Bamford SET On Thu, May 10, 2018 at 12:19 PM, Ed Kramer <[email protected]> wrote: > I agree. The loads given on the data sheets have safety factors > built-in. If for some reason you needed to do an engineering analysis of > that hanger, you’d have to contact Tolco for the load at which it failed > during testing. > > > > Ed Kramer > > Bamford Fire > > > > *From:* Sprinklerforum [mailto:[email protected]. > org] *On Behalf Of *Mike B Morey > *Sent:* Thursday, May 10, 2018 1:52 PM > *To:* [email protected] > *Subject:* Re: Hanger Loading > > > > I believe if you look at the wording of the standard the only time the > phrase 5 times the weight of the water filled pipe plus 250 pounds occurs > is in situations that require an "engineered" solution to hanging. EG > multiple system supports, pipe stands outside the scope of NFPA etc. I > can't draw a neat and tidy straight line to an answer but my understanding > is a listed hanger ring fore fire protection is listed per NFPA spacing for > a given pipe size. > > ------------------------------ > > > *Mike Morey* > *CFPS 3229 • NICET S.E.T. 123677* > *Project Manager* • Fire Protection Group > *Shambaugh & Son, LP **an EMCOR Company* > 7614 Opportunity Drive • Fort Wayne, IN • 46825 > *direct *260.487.7824* / cell *260.417.0625* / fax *260.487.7991 > *email *[email protected] > > > > > > > > From: "Jerry Van Kolken" <[email protected]> > To: <[email protected]> > Date: 05/10/2018 01:39 PM > Subject: Hanger Loading > Sent by: "Sprinklerforum" <sprinklerforum-bounces@lists. > firesprinkler.org> > ------------------------------ > > > > > BE ADVISED - This email originated outside EMCOR. > > > I’m doing this right? > > I’m looking at a Tolco Fig 200-2 hanger ring. > > The max load is 400lbs. > > 400 – 250 = 150 / 5 = 30lbs > > 2” sch ~5.13lbs > > This means if I use this ring I will have to space my hangers about 5’8” > on center. > > Jerry Van Kolken > *Millennium Fire Protection Corp.* > 2950 San Luis Rey Rd. > Oceanside, CA 92058 > (760) 722-2722 FX 722-2730 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists. > firesprinkler.org_listinfo.cgi_sprinklerforum- > 2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r= > z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m= > N3WrelPA9HyxwAUW1pXezh1NhirVM42OLEaRG-QQzzM&s= > VdvHTs70EM6mYEHE25sbxz6eV9I--K3jKw9VtzhtJUM&e= > > This message is for the named person's use only. It may contain > confidential, proprietary or legally privileged information. No > confidentiality or privilege is waived or lost by any mistransmission. If > you receive this message in error, please immediately delete it and all > copies of it from your system, destroy any hard copies of it and notify the > sender. You must not, directly or indirectly, use, disclose, distribute, > print, or copy any part of this message if you are not the intended > recipient. > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org