I bet if you dig into these specs, you'll find some safety factors:

Federal Specification A-A-1192A (Type 10)
WW-H-171-E (Type 10),
ANSI/MSS SP-58 (Type 10). UL Listed and FM Approved (Sizes 3⁄4" - 8")

Table 9.2.2.1(a)       2”   hanger every 15’
Table A.9.3.5.9        2” sch 40   5.13 lbs/ft

15’ x 5.13 =  76.95 lbs @ hanger
77 lbs x 5 =  385 lbs + 250  = 635 lbs

The 300 lb or 400 lb rating on hanger spec sheets is Low Number and the
Tested weight is divided by a safety factor.

Chuck Bamford SET





On Thu, May 10, 2018 at 12:19 PM, Ed Kramer <[email protected]> wrote:

> I agree.  The loads given on the data sheets have safety factors
> built-in.  If for some reason you needed to do an engineering analysis of
> that hanger, you’d have to contact Tolco for the load at which it failed
> during testing.
>
>
>
> Ed Kramer
>
> Bamford Fire
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Mike B Morey
> *Sent:* Thursday, May 10, 2018 1:52 PM
> *To:* [email protected]
> *Subject:* Re: Hanger Loading
>
>
>
> I believe if you look at the wording of the standard the only time the
> phrase 5 times the weight of the water filled pipe plus 250 pounds occurs
> is in situations that require an "engineered" solution to hanging.  EG
> multiple system supports, pipe stands outside the scope of NFPA etc.  I
> can't draw a neat and tidy straight line to an answer but my understanding
> is a listed hanger ring fore fire protection is listed per NFPA spacing for
> a given pipe size.
>
> ------------------------------
>
>
> *Mike Morey*
> *CFPS 3229 • NICET S.E.T. 123677*
> *Project Manager* • Fire Protection Group
> *Shambaugh & Son, LP **an EMCOR Company*
> 7614 Opportunity Drive • Fort Wayne, IN • 46825
> *direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
> *email *[email protected]
>
>
>
>
>
>
>
> From:        "Jerry Van Kolken" <[email protected]>
> To:        <[email protected]>
> Date:        05/10/2018 01:39 PM
> Subject:        Hanger Loading
> Sent by:        "Sprinklerforum" <sprinklerforum-bounces@lists.
> firesprinkler.org>
> ------------------------------
>
>
>
>
> BE ADVISED - This email originated outside EMCOR.
>
>
> I’m doing this right?
>
> I’m looking at a Tolco Fig 200-2 hanger ring.
>
> The max load is 400lbs.
>
> 400 – 250 = 150 / 5 = 30lbs
>
> 2” sch ~5.13lbs
>
> This means if I use this ring I will have to space my hangers about 5’8”
> on center.
>
> Jerry Van Kolken
> *Millennium Fire Protection Corp.*
> 2950 San Luis Rey Rd.
> Oceanside, CA 92058
> (760) 722-2722 FX 722-2730
>  _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.
> firesprinkler.org_listinfo.cgi_sprinklerforum-
> 2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=
> z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=
> N3WrelPA9HyxwAUW1pXezh1NhirVM42OLEaRG-QQzzM&s=
> VdvHTs70EM6mYEHE25sbxz6eV9I--K3jKw9VtzhtJUM&e=
>
> This message is for the named person's use only. It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission. If
> you receive this message in error, please immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender. You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to