Wouldn’t the trailer storage bring it up to EH2?
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (ofc)
  
860-553-3553 (fax)
  
860-608-4559 (cell)
  
  
  
  

  
  
>   
> On May 17, 2018 at 9:47 AM,  <John Irwin (mailto:john.ir...@dynafire.com)>  
> wrote:
>   
>   
>       
>   
>
> Here’s the situation … I have a 5,000 sqft, (currently) ordinary hazard mixed 
> use space. The new tenant intends to store two emergency disaster management 
> trailers in this space. However, along two walls, they want to put a 3-teir 
> rack with storage up to 20’ in height. TOS in the center of the unit is 23-9.
>
>   
>
>   
>
>   
>
> The racks will contain a mix of group A plastic, emergency supplies in 
> plastic totes, with lids, on non-combustible pallets.
>
>   
>
>   
>
>   
>
> Do I really have to upgrade this entire space from OH II to .6/2000?
>
>   
>
>   
>
>   
>
> Do I tell them they should just not store over 12’?
>
>   
>
>   
>
>   
>
> John Irwin
>
>   
>
> Fire Sprinkler Specialist
>
>   
>
> DynaFire, Inc. – “Same Day – Next Day”
>
>   
>
> 727-282-9243 – Cell
>
>   
>
>   
>
>   
>
>  “A customer is the most important visitor on our premises. He is not 
> dependent on us. We are dependent on him. He is not an interruption on our 
> work. He is the purpose of it. He is not an outsider on our business. He is a 
> part of it. We are not doing him a favour by serving him. He is doing us a 
> favour by giving us an opportunity to do so.”
>
>   
>
>   
>
>   
>
>   
>
>   
>  _______________________________________________ Sprinklerforum mailing list 
> Sprinklerforum@lists.firesprinkler.org 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
     