Light hazard only and yes 60" rule went into effect a few years ago. 

Thermo-Tile is the only band I know of.

King and Company 
PO Box 10
Clarksville AR 72830
United States of America
‭+1 (800) 643-9530‬
http://www.thermo-tile.com

And I will give them one heart, and I will put a new spirit within you; and I 
will take the stony heart out of their flesh, and will give them an heart of 
flesh
Eze 11:19

> On May 31, 2018, at 11:00 AM, Kyle.Montgomery <[email protected]> 
> wrote:
> 
> I’ve been searching around a little bit, but figured I would ask here, anyone 
> have experience with installing these under sprinklers?
>  
> I’m working with an architect whose client needs to install these polystyrene 
> ceiling tiles that have been tested to drop-out in the case of a fire. 
> They’re not doing it to try to save costs, apparently the spec for the 
> product they assemble requires a “clean” environment which drives this.
>  
> I’m having trouble finding good information about this. The NFPA requirements 
> are pretty straightforward, but I’m seeing some conflicting issues in some of 
> the other information I can find:
>  
> 1.       NFPA 13 does not permit QR heads above these ceilings (unless the 
> ceiling is specifically listed for them), yet some of the other information 
> I’ve found suggests that they can only be used in light hazard areas.
> 2.       I’ve seen some information suggesting that the sprinklers need to be 
> within 60” of these ceilings, but NFPA 13 makes no mention of that. Is that 
> an actual requirement?
>  
> Thanks guys. Any info helps.
>  
> -Kyle M
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to