What if fewer sprinklers open than in your design area?  The pump and water 
supply aren’t going to know what the minimum sprinkler demand is and magically 
hold to that point while discharging no more.

 

I know you are well aware of this.  The sprinkler calculations are demand calcs 
that give minimums.  You can run supply calcs to determine what pressures and 
flows you can expect with the full water supply discharging.

 



Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:[email protected]> email:[email protected]

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
 http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

From: Sprinklerforum <[email protected]> On Behalf 
Of Prahl, Craig/GVL
Sent: Wednesday, June 27, 2018 8:22 AM
To: [email protected]
Subject: Real system pressures versus the calculations

 

I have a system that was originally designed with a fire pump taking suction 
from an elevated municipal water tank.  At some point in time the system source 
was changed from the tank to a municipal water supply.  This change has 
resulted in the system pressures being well over 200-250 psi.  So far nothing 
has blown out, yet but numerous buildings and underground were built based on 
standard pressure rated components.

 

The thought for the day is this, when you run a calculation, the output will 
show the minimum required pressure at the hydraulically most remote sprinkler 
that is required to provide the design flow rate.  The calculations also show 
the deviation between Required and Available system pressures.  So, when the 
fire pump kicks on, what the system ACTUALLY sees is the rated pressure of the 
pump being introduced into the system, not the minimum required pressure that 
is shown in the calculations, Agreed?

 

If it is stated that in the calculations that the pressure at the sprinklers on 
an upper floor will be less than 175 psi but those on the lower floor will be 
greater is it safe to assume based on the ACTUAL pressures coming out of the 
pump that the entire system will likely see pressures exceeding 175 psi?  

 

Looking for some thoughts.  

 

Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
[email protected] <mailto:[email protected]>  |  
<http://www.jacobs.com/> www.jacobs.com

 

________________________________________________________________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to