Pendent sprinklers can be 1 to 12 inches below ceiling. And if you have ever heard of a 401 canopy, that would work quite well.
Depending on size of room I would be more inclined to space the sprinklers away from the conduit and add a few sprinklers if necessary. Just a couple thoughts / ideas. Jeff On Thu, Jun 28, 2018 at 4:56 PM, Jerry Van Kolken <[email protected]> wrote: > I’m protecting a server room. And they are installing sets of conduit > piping close to the ceiling. These are 1” to 1-1/2” conduit with about 1” > gap between them. There are a set of 8 double stack sandwiching unistrut. > I’m thinking of the open grid ceiling when considering whether or not I > need to adjust my sprinkler locations, but I’m not sure this applies in > this case. Is there a better reference to look at for this type of > situation? > > > > Jerry Van Kolken > > *Millennium Fire Protection Corp.* > > 2950 San Luis Rey Rd. > > Oceanside, CA 92058 > > (760) 722-2722 FX 722-2730 > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >