Not possible to just raise pump up more? 6 inches or so?

On Mon, Jul 9, 2018 at 2:43 PM, Brian Harris <[email protected]>
wrote:

> There’s currently a flanged 8x6x6 reducing tee bolted to the stub-up. I
> need to raise that tee 2-1/2”.
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssytemsinc.com <http://bvssystemsinc.com/>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *MFP Design, LLC
> *Sent:* Monday, July 09, 2018 3:42 PM
>
> *To:* [email protected]
> *Subject:* RE: Flange Spacers?
>
>
>
> *It is just a short “main” with a size on size welded outlet.  Don’t we do
> that all the time?*
>
>
>
> [image: MFP_logo_F]
>
> Travis Mack, SET
>
> MFP Design, LLC
>
> 3356 E Vallejo Ct
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> email:[email protected]
>
>
>
> http://www.mfpdesign.com
> <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
>
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>
> LinkedIn: https://www.linkedin.com/in/travismack
> <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
>
>
>
> *“**The bitterness of poor quality remains long after the sweetness of
> low price is forgotten.**”*
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *Brian Harris
> *Sent:* Monday, July 9, 2018 12:41 PM
> *To:* [email protected]
> *Subject:* RE: Flange Spacers?
>
>
>
> Jeff-
>
> Would a fabricated Tee be listed though?
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssytemsinc.com <http://bvssystemsinc.com/>
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org <[email protected]>] *On Behalf Of *Jeff
> Normand
> *Sent:* Monday, July 09, 2018 3:34 PM
> *To:* [email protected]
> *Subject:* Re: Flange Spacers?
>
>
>
> Fabricate a flanged tee or elbow.
>
>
>
> On Mon, Jul 9, 2018 at 2:21 PM, Brian Harris <[email protected]>
> wrote:
>
> Anybody ever use a flange spacer ring? We have a job with a diesel pump
> and the underground stub-ups were put in at the wrong elevation. Need to
> make up 2-1/2" in the vertical.
>
>
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> Design Manager
>
> bvssystemsinc.com
>
> Phone: 704.896.9989
>
> Fax: 704.896.1935
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to