Thanks Larry!!
Maybe there would be a problem with the bolt kit? Brad From: Sprinklerforum [mailto:[email protected]] On Behalf Of Larry Keeping Sent: Tuesday, July 10, 2018 10:40 AM To: [email protected] Subject: RE: Grooved Flange Adapters I agree, the dimensions don’t work, but also, while it doesn’t say why, the Vic-Flange Adapter Notes in Vic. data sheet 10.04 says “FireLock Flange adapter should not be used on FireLock fittings.” Larry Keeping From: Sprinklerforum [mailto:[email protected]] On Behalf Of Kenneth Berman Sent: July-10-18 11:34 AM To: [email protected] <mailto:[email protected]> Subject: Re: Grooved Flange Adapters there's not enough clearance for two on the same 90, and the adapter / coupling combo must use a 009 (slip in) coupling. On Tue, Jul 10, 2018 at 10:29 AM, Brad Casterline <[email protected] <mailto:[email protected]> > wrote: Do 6” Grooved Flange Adapters work on both ends of 6” Firelok 90s? Thanks, Brad _______________________________________________ Sprinklerforum mailing list [email protected] <mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org