Thanks Larry!!

 

Maybe there would be a problem with the bolt kit?

 

Brad

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Larry Keeping
Sent: Tuesday, July 10, 2018 10:40 AM
To: [email protected]
Subject: RE: Grooved Flange Adapters

 

I agree, the dimensions don’t work, but also, while it doesn’t say why, the 
Vic-Flange Adapter Notes in Vic. data sheet 10.04 says “FireLock Flange adapter 
should not be used on FireLock fittings.”

 

Larry Keeping

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kenneth Berman
Sent: July-10-18 11:34 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: Re: Grooved Flange Adapters

 

there's not enough clearance for two on the same 90, and the adapter / coupling 
combo must use a 009 (slip in) coupling.

 

On Tue, Jul 10, 2018 at 10:29 AM, Brad Casterline <[email protected] 
<mailto:[email protected]> > wrote:

Do 6” Grooved Flange Adapters work on both ends of 6” Firelok 90s?

 

Thanks,

 

Brad 