Rod:
Marriott can be tricky. Yes, that is a public space. They have only recently allowed the use of concealed sprinklers. In the architects I have worked with on these properties, we have still been doing recessed sprinklers and not concealed. The 2015 edition of Module 14 is where they started allowing concealed sprinklers. Prior to that, they prohibited the use of concealed sprinklers. I guess in a round about way, if you are held to the specifications, then I think they have you on that one, especially if you have concealed sprinklers in the remainder of the public spaces. Travis Mack, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:email:[email protected]> email:[email protected] <https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi gn.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4 2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2 FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b 4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166 77342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C 14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2 wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0> https://www.hightail.com/u/MFPDesign LinkedIn: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77% 7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0> https://www.linkedin.com/in/travismack "The bitterness of poor quality remains long after the sweetness of low price is forgotten." From: Sprinklerforum <[email protected]> On Behalf Of Rod DiBona Sent: Wednesday, July 25, 2018 11:27 AM To: [email protected] Cc: Kyle Watson <[email protected]> Subject: definition of public space We have a Marriott hotel where we installed a dry system with SR Dry pendants in the porte cochere. The specifications call for concealed heads in all public areas. The specifications also refer to Module 14 that says that concealed heads are not preferred. We submitted the SR dry heads and got approved drawings. Now after installation and the stucco ceiling finished the GC has directed us to remove and replace with concealed heads per the specifications. Do you consider the porte cochere to be a public space? All definitions I have found seem to indicate that it is. For those out there doing Marriott properties have you seen these done with SR or have they all been concealed? Thanks. Rod at Rapid
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org