Rod:

 

Marriott can be tricky.  Yes, that is a public space.  They have only
recently allowed the use of concealed sprinklers.  In the architects I have
worked with on these properties, we have still been doing recessed
sprinklers and not concealed.  The 2015 edition of Module 14 is where they
started allowing concealed sprinklers.  Prior to that, they prohibited the
use of concealed sprinklers.

 

I guess in a round about way, if you are held to the specifications, then I
think they have you on that one, especially if you have concealed sprinklers
in the remainder of the public spaces.

 



Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:[email protected]> email:[email protected]

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesi
gn.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da4
2e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2
FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0> http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebo
ok.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b
4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166
77342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

From: Sprinklerforum <[email protected]> On
Behalf Of Rod DiBona
Sent: Wednesday, July 25, 2018 11:27 AM
To: [email protected]
Cc: Kyle Watson <[email protected]>
Subject: definition of public space

 

We have a Marriott hotel where we installed a dry system with SR Dry
pendants in the porte cochere. The specifications call for concealed heads
in all public areas. The specifications also refer to Module 14 that says
that concealed heads are not preferred. We submitted the SR dry heads and
got approved drawings. Now after installation and the stucco ceiling
finished the GC has directed us to remove and replace with concealed heads
per the specifications. Do you consider the porte cochere to be a public
space? All definitions I have found seem to indicate that it is. For those
out there doing Marriott properties have you seen these done with SR or have
they all been concealed? Thanks.

 

Rod at Rapid

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to