Storage units 200 -600 SF per unit covered by metal screen at 10 Ft. AFF
with metal sided partitions.

Household goods, mattresses, foam  cushions on sofas. Class 3-Class A
plastic.

Roof sprinklers at 14FT is a pipe schedule system from 1956.

This is a change of occupancy.

 

The existing pipe schedule system is not adequate for the hazard.

The sprinkler system should be revised and brought up to NFPA design
density.

Is the appropriate design based on Class A plastic or something less?

I could not find anything in archives.

 

Art Tiroly

ATCO Fire Protection

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 



---