I think the code says if the highest floor elevation exceeds 30' above the
lowest level of fire department access, stand pipes are required. Not
quoting just remembering off the top of my head.

On Wed, Aug 8, 2018, 5:55 PM Taylor Schumacher <tay...@sfsprinkler.com>
wrote:

> I have an AHJ that is adamant that a 3-story 13R project I have requires
> Class I standpipes because the underground parking level will exceed the
> 30’ height requirement. I have always viewed these heights as from the
> parking lot closest to main entry or where the FDC is located rather than
> the fire truck driving into the garage. Have I been looking at this wrong?
>
>
>
>
>
> *Taylor Schumacher*
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to