I believe your best opportunity is in 8.15.1.2.5 if you can convince
yourself that the C-channel is equivalent to wood joist or other solid
construction. However I'd be extra cautious in that assessment as you
may be required to provide a minimum 3,000 ft² remote area per 11.2.3.1.5.1.
quick thoughts,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> ***
On 08/22/2018 1:00 PM, [email protected] wrote:
Am I missing something or is there not an exception for protecting
comb concealed spaces with Metal C Channel joists and plywood on the
top and bottom?