NFPA 20 4.26 requires a Jockey (Make-Up) Pump. Provided the main pump is 
pressure activated.



​David Victor
VSC Fire & Security, Inc.
10640 Iron Bridge Road, Suite G
Jessup, 
MD
 
20794
[email protected] | 
vscfs.com
301-575-1500 Office
 | 
301-575-1501 Fax
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Thursday, August 30, 2018 5:06 AM
To: [email protected]
Subject: Re: No Jockey Pump


Without a jockey pump, every time there is a pressure drop the pump would start.



Mike

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Bruce Verhei <[email protected]<mailto:[email protected]>>
Sent: Wednesday, August 29, 2018 10:24 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Re: No Jockey Pump

So why do we use jockey pumps? Wouldn't one of Mike H's flow switches alway be 
cheaper?

Best.

Bruce Verhei

On Aug 29, 2018, at 19:05, Larry Keeping 
<[email protected]<mailto:[email protected]>> wrote:

NFPA 20 has never mandated jockey pumps.



Back in the cycle for the development of the 1999 edition, in response to 
Proposal 20-36, the Committee Statement confirmed that "A pressure maintenance 
pump is not required by the standard. ..."



For the 2016 edition, some text was added, for the first time, to clarify that 
pressure maintenance is required for pressure-actuated fire pumps, but a jockey 
pump is not necessarily required to accomplish the task. Section 4.26.1 (c) 
allows "Another approved means that is not the main fire pump". And again, the 
Committee Statement confirmed "... a pressure maintenance pump may not 
necessarily be required and that other forms of pressure maintenance may be 
used. ...".



Larry Keeping







From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Thomas Reinhardt
Sent: August-29-18 5:15 PM
To: 
[email protected]<mailto:[email protected]>
Subject: No Jockey Pump



Hi group,

Found a 50 yr. old fire pump at a business that didn't have a jockey pump. Am I 
missing something. Thanks



Tom Reinhardt

Fire Inspector/Plan Reviewer

Skokie Fire Department

7424 Niles Center Road

Skokie, IL 60077

Office: 847-982-5342

[email protected]<mailto:[email protected]>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to