What Bruce said.  Both Code (intermediates) and Standard (floors) state what 
they state but also contain a provision that essentially says, “Or as required 
by the fire official…”   If you have any doubt, consult with and affirm the 
locations with the fire official.

I personally like the floor landings because it makes the floor control 
assemblies and drains easier on combined systems and most FDs we work with in 
the Southwest specify floor landings.  But we have more than a few that prefer 
the intermediates; this goes to department training practices and operational 
tactics so deference to the FD’s preference is paramount.

My 2¢ only,

[Steve Signature (3)]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bruce Verhei
Sent: Tuesday, September 11, 2018 2:00 PM
To: [email protected]
Subject: Re: Hose Connections - Main Stair Landings vs. Intermediate Landings

I’d contact local FD and see their requirements.

Floor below was long tradition. Dates back to standpipes being inserted into 
stairwell. Now you’re normally in a rated shaft. You don’t need a hose line to 
follow once you’re in the rated stairwell.

Best.

Bruce Verhei

On Sep 11, 2018, at 10:39, Steele, Andrew 
<[email protected]<mailto:[email protected]>> wrote:
It sort of matters; think firefighters flaking out no less than 100-feet of 
hose (maybe more) in the stairwell before charging the hose line with standpipe 
water.  This has to be laid neatly so it does tangle and kink on charging.  
Typically the FD will hook to the first outlet BELOW the level of the fire, but 
then lay ½ of the hose up the stair above the fire, then come back down, to 
make entry on fire floor (laying hose above so it’s easier to pull into the 
floor as they are crawling along).  Hooking below is so if things go really 
bad, the firefighters can hands on follow the hose out into the stairway and 
down, hopefully to a safer place.

The half-level provides for more hose reach into the actual floor.

Andrew Steele


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Trever Williams
Sent: Tuesday, September 11, 2018 1:35 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Hose Connections - Main Stair Landings vs. Intermediate Landings

From a practical standpoint does it matter if the hose connections in the 
stairwells are installed on the main floor landings or the intermediate 
landings?

I remember learning years ago that it really doesn’t matter, and in a fully 
sprinkled building it really, really doesn’t matter, but lately I’ve been 
encountering AHJs that seem to think it matters.

Trever Williams
Design Manager
Unlimited Sprinkler Fire Protection
130 Kristen Ln.
Wylie, TX 75098
214-349-8444 ex. 312 - Phone
214-349-8450 - Fax


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to