How do you get a building built in 67 that needs a 50 year test in 4 years when 
it is already 51 years old. Maybe it’s just time to change the heads. 
Bill

Sent from my iPhone

> On Sep 13, 2018, at 6:32 PM, Jamie Seidl <[email protected]> wrote:
> 
> To me this sounds like classic Solder creep.  The solder softens furring warm 
> conditions, and after many many (years) of hot days, you start to have heads 
> pop as the solder has finally given in to the pressure it has been holding 
> back.  I think your correction  on this would be glass bulb sprinklers.
> Jamie Seidl
> 
>> On Thu, Sep 13, 2018 at 5:20 PM Larry Block, Property Manager 
>> <[email protected]> wrote:
>> Hi to all!
>> 
>>  
>> 
>> I manage a number of most warehousing industrial parks around Los Angeles 
>> and only 1 of them has a problem with heads popping off for no apparent 
>> reason. We really need some help here in identifying the cause and its 
>> correction. Many have said to just replace them but who is to say that this 
>> will not happen again soon, if not later. The facts:
>> 
>>  
>> 
>> 1. Concrete tilt up bldg from 1967 with its roof at 20’ H.
>> 
>> 2. Heads are Reliable model C with the fusible link
>> 
>> 3. Heads will get the 50 year  UL testing in 4 years (though I assume the 
>> 165degF rating is not relevant here)
>> 
>> 4. We have lost 7 heads over 15 years, with 3 in the last 4 months!
>> 
>> 5. The link assemblies are never found but the remaining “rings” show no 
>> issues. The bronze seats
>> 
>> of the head’s  water port are always in perfect condition.
>> 
>> 6. We see that the head’s “knuckle” that is opposite the fusible link is 
>> usually perfectly aligned,
>> 
>>               but a few of them are offset up to a 1/16” and it appears that 
>> when they move like that,
>> 
>> they are rotating in an arc from the pivot points .
>> 
>> 7. The water utility swears that at the time of these events, there are no 
>> pressure surges.
>> 
>> 8. No more than one head has ever gone off at a time and are not just at one 
>> location or riser.
>> 
>> 9. A nearby similar bldg of ours  from 1968 with the same heads has never 
>> had one such event.
>> 
>>  
>> 
>> We have entertained the possibility of water pressure, birds, electrolysis, 
>> dezincification, vibration and are at a loss.
>> 
>>  
>> 
>> Any helpful thoughts?
>> 
>>  
>> 
>> Thanks,
>> 
>>  
>> 
>> Larry Block, Property Manager
>> 
>>  
>> 
>> 
>>      Virus-free. www.avast.com
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> -- 
>      \ \
>      (o>  --  If life were easy...
>  \ \_/ /)                           It'd be called your mom...
>   \_/_)
>    _|_
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to