I believe this is spelled out in the NFPA 14 handbook.  You will need to do 2 
sets of calculations.  Where you only have 2 standpipes, you calculate the 750 
gpm.  When you get down to the level with 3 standpipes, you do another calc 
that goes to 1000 gpm.

 



Travis Mack, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:email:[email protected]> email:[email protected]

 

 
<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.mfpdesign.com%2F&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=HJ8OA4xyeHAoxXNz5mu%2FYfycgtd5nsFrrpvzulZiNkQ%3D&reserved=0>
 http://www.mfpdesign.com

 
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FMFP-Design-LLC%2F92218417692&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=H%2BwdcgK8DLGBcNoqJEvUrzsXngySwkX56Vgf9gM9EGk%3D&reserved=0>
 https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

From: Sprinklerforum <[email protected]> On Behalf 
Of Dewayne Martinez
Sent: Wednesday, September 19, 2018 12:09 PM
To: [email protected]
Cc: Dewayne Martinez <[email protected]>
Subject: multi-height standpipes

 

I have a high rise which contains 3 standpipes.  Two of them go up 25 stories 
and the third only 4 stories.  When I calculate them do I pick up 2@ 250gpm on 
the most remote high standpipe followed by 250 on the remaining stairwells 
including the low one or just the two high ones?  To complicate the matter even 
more the high standpipes would not have a pressure reducing hose valves in the 
calculation but the low standpipe would need one.

Thanks,  

 

Dewayne Martinez

Fire Protection Design Manager

 

TOTAL Mechanical

Building Integrity


W234 N2830 Paul Rd.
Pewaukee, WI  53072

 <mailto:[email protected]> [email protected]

Ph:  262-522-7110

Cell: 414-406-5208

 <http://www.total-mechanical.com/> http://www.total-mechanical.com/ 

           



 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to