I would say that test pipe would do the job, based on what it says in 6.10.4:

6.10.4 When the drain required in 6.9.1 is arranged as a test connection, a 
separate test connection shall not be required.

Larry Keeping

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of James Litvak
Sent: September-20-18 11:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: 13R Test and Drain Question

On a 13R system, 6.9.2 specifies that the drain piping must be at least 1" 
nominal size. If a residential system riser has a 1" drain pipe to outside that 
has either a test valve with a 1/2" orifice or terminates at a broken sprinkler 
with a 1/2" orifice, does that drain piping still meet the requirements of 
6.9.2?