The contractor on our project wants to complete the fire pump acceptance 
testing soon but the generator is not on site yet.  NFPA 20 (2013 ed) states in 
14.2.8 that “On installations with an alternate source of power and an 
automatic transfer switch, loss of primary source shall be simulated and 
transfer shall occur while the pump is operating at peak load.”  Would it be 
acceptable to connect a temporary generator to complete the acceptance testing 
and then install the “permanent” generator at a later date without needing to 
redo any tests?

The standard doesn’t address this specifically that I can find, but in my mind 
the test is performed to ensure the transfer switch will operate correctly and 
the testing of the actual generator is a separate task, so it wouldn’t be 
crucial to have the permanent generator in place.  It would make sense that the 
temporary generator would need to be sized the same as the permanent generator 
but wondering if anyone can tell me if this is acceptable?

Other food for thought…wouldn’t the above scenario be the same as if the 
generator fails 6 months from now and gets replaced?...would the fire pump 
starts and flow testing be required to be performed again?

Thank you.

Reed Roisum


Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
KFIengineers.com<http://www.kfiengineers.com>

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to