We have used both wax coated and poly coated.  The problem with wax, is the wax 
coating is comprimised by the wrenches.  That does not seem to be a problem 
with poly.  We always leave a couple of new wrenches in the head box.  For our 
wrecnhes, I take  a new head and at least 2 wrenches to the local machine shop. 
 He hard faces the wrench and then machines the wrench to fit the head.  

From: Kyle.Montgomery 
Sent: Tuesday, October 02, 2018 3:37 PM
To: [email protected] 
Subject: RE: Fire sprinklers in harsh coastal environments

Those are pretty expensive though, aren’t they? If you look at the sprinkler 
cut sheets from Reliable (and others) they generally list the White Polyester 
heads as “corrosion resistant” and we’ve used those. I don’t think the white 
polys cost that much more than your standard sprinkler. 

 

We’ve used these in areas, like Camp Pendleton Hospital Parking Garage, which 
is exposed and pretty close to the ocean. Admittedly, I haven’t gone back years 
later to check on their condition.

 

-Kyle M

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Charles Thurston
Sent: Tuesday, October 2, 2018 12:49 PM
To: [email protected]
Subject: [EXTERNAL] RE: Fire sprinklers in harsh coastal environments

 

We have used Nickle Teflon under buildings where the guys got to look at the 
ocean while installing them and they still look good 6 years later.

 

 

Side Note I still have the old wax warmer and about 5 pounds of BeesWax we used 
to use for dipping them in.

 

 

 

Best regards,

Charles Thurston                          [email protected]

MYRTLE BEACH FIRE SAFETY GROUP

A Division of Pye-Barker Fire Safety

1445 Cannon Road

Myrtle Beach, SC 29577

(843) 916 - 8787

(843) 839 - 3473 facsimile

 



 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gabe White
Sent: Tuesday, October 02, 2018 2:50 PM
To: [email protected]
Subject: Re: Fire sprinklers in harsh coastal environments

 

Thanks Everyone. Very helpful.

 

 

 

From: Sprinklerforum <[email protected]> on behalf 
of Steve Leyton <[email protected]>
Reply-To: "[email protected]" 
<[email protected]>
Date: Tuesday, October 2, 2018 at 11:23 AM
To: "[email protected]" 
<[email protected]>
Subject: Re: Fire sprinklers in harsh coastal environments

 

Yes! Years ago, it wasn't uncommon for contractors to shop-dip sprinklers in 
wax before installing but no more. ALL finishes must be listed and 
factory-applied.

 

 

 

Steve Leyton  

 

(Sent from my phone; please excuse typos and voice text corruptions.)

 

 

 

-------- Original message --------

From: Gabe White <[email protected]> 

Date: 10/2/18 2:20 PM (GMT-05:00) 

To: [email protected] 

Subject: Re: Fire sprinklers in harsh coastal environments 

 

Do they need a UL rating to be certified corrosion resistant? Per NFPA 13 
(6.2.6.1)

 

 

 

From: Sprinklerforum <[email protected]> on behalf 
of Fpdcdesign <[email protected]>
Reply-To: "[email protected]" 
<[email protected]>
Date: Tuesday, October 2, 2018 at 11:16 AM
To: Sprinklerforum <[email protected]>
Subject: Re: Fire sprinklers in harsh coastal environments

 

Wax coated. Perhaps some of the pvc coated but you would need to check

 

  On Oct 2, 2018 at 2:05 PM, <Dale Wingard> wrote:

  Yes.  NFPA 13 (2016) 6.2.6.1  

   



   

  From: Sprinklerforum <[email protected]> On 
Behalf Of Gabe White
  Sent: Tuesday, October 2, 2018 1:01 PM
  To: [email protected]
  Subject: Fire sprinklers in harsh coastal environments

   

  Does anyone know of a requirement for fire sprinklers to be of a certain type 
or material in harsh coastal environments to prevent corrosion from the salt 
air?

   

   

  _______________________________________________ Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 



--------------------------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to