2016 edition doesn't say that either.  Performance information and listing 
limitations will be published by the manufacturer and you should seek 
affirmation of those metrics from them.

9.2.1.3.3* Flexible Sprinkler Hose Fittings.
9.2.1.3.3.1 Listed flexible sprinkler hose fittings and their anchoring
components intended for use in installations connecting
the sprinkler system piping to sprinklers shall be installed
in accordance with the requirements of the listing,
including any installation instructions.

9.2.3.4.4.4 Unless flexible sprinkler hose fittings in accordance
with 9.2.1.3.3.1 are used, the hanger closest to the sprinkler
shall be of a type that prevents upward movement of the
pipe.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Thursday, October 25, 2018 8:32 AM
To: Sprinkler Forum
Subject: NFPA 13, 2016


Can someone send me a copy of Sections 9.2.3.4.4.4 and 9.2.1.3.3.1 please?



Local AHJ is using NFPA 13,2010 and it doesn't state that Flex heads prevent

upward movement when the branch line has 100 psi or greater pressure.



What he is looking for is a copy of the page from NFPA 13,2016.





Thanks



Mike