This is a 55 year old pipe schedule system 130 SF head. This is a change of use 
and requires a density design.

Existing system does not work hydraulically.

Therefore I am creating a calculated system which requires replacing small pipe 
at end of BL’s with 1.5”.



Is this not necessary?





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell









From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Monday, October 29, 2018 6:42 PM
To: [email protected]
Subject: Re: Pipe Sch Water Supplies



Not sure East you mean:  Not meant fro warehousing but you are converting from 
a F occupancy to warehousing.  Nonetheless,tyhere is no schedule for storage.  
That was deleted many cycles ago.





Roland Huggins, PE - Senior VP Engineering

American Fire Sprinkler Assn.

Dallas, TX

http://www.firesprinkler.org <http://www.firesprinkler.org/>



Fire Sprinklers Saves Lives









On Oct 29, 2018, at 2:32 PM, Art Tiroly <[email protected]> wrote:



What is the sprinkler spacing 90-130 SF?

Light or OH?



Not meant for warehousing.

I'm working on one now converting from factory to warehousing.

1”, 1”, 1-1/4” does not calculate at 130 SF/head.

Up sizing to get .20/1500 for 8-10’ storage of household furnishings and 
storage.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [ <mailto:[email protected]> 
mailto:[email protected]] On Behalf Of Mark Eckard
Sent: Monday, October 29, 2018 4:48 PM
To:  <mailto:[email protected]> 
[email protected]
Subject: Pipe Sch Water Supplies



I remember in some of the older NFPA-13s there were minimum water supply 
requirements for Pipe Scheduled systems.  Does any one have that information?  
I thought I had it, but I cant seem to locate it.



Thank You



Mark E. Eckard SET

<image001.jpg>

Fire Protection Services, LLC

2126 US Hwy. 41 North

Perry, GA 31069

Office: 478-987-7319 (Perry) or (770) 702-0965 (Metro Atlanta)

Mobile: 478-244-6653

SYL-216






 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=icon>

Virus-free.  
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient&utm_term=link>
 www.avast.com

_______________________________________________
Sprinklerforum mailing list
 <mailto:[email protected]> 
[email protected]
 <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to