I would think that QR is OK but that C-Factor should still be reduced (100).

What does the rest of the forum say?

-Kyle M

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bob Knight
Sent: Thursday, November 1, 2018 3:35 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] Single Preaction System

Thanks Kyle, I had read that, but missed the take away.  It looks like I should 
have taken away that I don't need the area increase.
What about C Factors, are reductions, etc...?  I would assume that since it's 
calc'ed as a wet system that C120 and reductions would be okay.

Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057

From: Kyle.Montgomery [mailto:kmontgom...@aerofire.com]
Sent: Thursday, November 01, 2018 4:22 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>;
 b...@firebyknight.com<mailto:b...@firebyknight.com>
Subject: RE: [EXTERNAL] Single Preaction System

See 11.2.3.2.5 and A.11.2.3.2.5.

-Kyle M

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Kyle.Montgomery
Sent: Thursday, November 1, 2018 3:19 PM
To: b...@firebyknight.com<mailto:b...@firebyknight.com>; 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: [EXTERNAL] Single Preaction System

One of the biggest impacts is that calculating as a dry system means you have 
to increase remote area size by 30%, but you don't have to do that if you can 
calculate as wet.

-Kyle M

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bob Knight
Sent: Thursday, November 1, 2018 2:59 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] Single Preaction System

I'm looking at a cut sheet for an Electric actuated single preaction system.  
It makes one statement that I haven't been able to find any other info, "In 
order for a single interlock preaction system to be hydraulically calculated as 
a wet pipe system, as opposed to a dry pipe sprinkler system, the detection 
system must be designed to operate sooner than the automatic sprinklers on the 
sprinkler piping."
I understand the operating part, but I swore that NFPA 13 addressed this "wet 
system" allowance but I can't find it.  I've looked back to the 2002 edition, 
but I can't find anything.  What exactly does it mean to be able to calculate 
as a wet pipe system?
Do I use C120, Design  Area  Reduction for QR, etc...?


Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057