For the venting requirement, NFPA 22 section 4.15 will provide some
guidance.

 

Ed K

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of John Irwin
Sent: Friday, November 02, 2018 7:16 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Always something new ... Dry hydrant?

 

Matt,

 

The tanks are 16.5' tall and the outlet is 6" from the base. This is going
to result in positive pressure at the pump inlet. What I wonder is if I can
get 784 gallons from those (4) 3" outlets.

 

Also, I agree that tanks need venting, but is there direction on how much
venting?

 

What standard am I using to design this contraption? Is it 1142 for a dry
hydrant?

 

John Irwin

Quick Response Fire Protection

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Matt
Grise
Sent: Friday, November 2, 2018 8:07 AM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: Always something new ... Dry hydrant?

 

It might be a good idea to perform a hydraulic analysis to see how much
water can be drawn through those 3" outlets. The pump that the FD is using
likely has minimum supply pressure (1/2psi or so). If you need (x) psi at
the pump suction flange, and you have (y) psi at the tank discharge (from
gravity/water level elevation), then you can flow (z) gpm through the piping
network before you lose too much pressure and start cavitating the pump.

 

I would definitely vent the tanks!

 

Matt 

 

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of John
Irwin
Sent: Friday, November 02, 2018 6:43 AM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: Always something new ... Dry hydrant?

 

Ok so here's something new for me . the situation .

 

Client has a client who is using a temporary, tent structure for storage.
And right now they are using mobile fracing water containers to supply what
I assume would be classified as a dry hydrant. The fire marshal wants
something a little more permanent. The property owner is supplying (4)
12,500 gallon water tanks. They appear to each (2) 3" threaded outlets on
them. Whether or not these tanks are acceptable per NFPA 22 isn't in my
scope. I will make some observations to them but that's about the extent of
that.

 

What they are asking of me: Design the manifold system to connect these
tanks and feed a 5" Stortz FDC for the fire department to use as a water
source in case of fire. It appears that the AHJ is requesting 784GPM for 60
minutes for a total of 47,040 gallons.

 

In which standard do I turn to for the required piping configuration for
this and how do prove that I can supply 784 gallons in a minute through
these (4) 3" outlets?

 

Other musings . I doubt there are vortex plates in these tanks. What's going
to happen? - Is there a venting requirement to keep the fire department from
imploding these tanks with their truck?

 

I'm looking forward to hearing your thoughts on this.

 

 

John Irwin

Branch Manager - West Coast