Now there’s a good question. I assumed ceramic or porcelain but obviously there 
are a lot of other types.

RFI

John Irwin
Quick Response Fire Protection

From: Sprinklerforum <[email protected]> On Behalf 
Of Fpdcdesign
Sent: Monday, November 5, 2018 4:10 PM
To: Sprinklerforum <[email protected]>
Subject: Re: Storage Density

What are the floor tiles made of?



On Nov 5, 2018 at 4:08 PM, <John Irwin<mailto:[email protected]>> 
wrote:
Building height = 29’
Let’s say storage to 25’ (single or double rows, open grate)
Floor tiles in plastic wrapped boxes on open slat wood pallets.

I am referencing Table 5.6.3.2 and calling these Class II Commodity (housing 
materials)

Now referencing 16.2.1.3.2(b) - .33/3000 with high temperature sprinklers at 
the roof.

NFPA 13 2016 edition.

Anyone disagree?


John Irwin
Branch Manager – West Coast
Quick Response Fire Protection
[email protected]<mailto:[email protected]>
CELL – 727-282-9243

_______________________________________________ Sprinklerforum mailing list 
[email protected]<mailto:[email protected]>
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to