Are you allowed to use intermediate sprinklers everywhere? In 13 Section 
8.3.2.1 seems to interchange the use of intermediate and ordinary, but table 
6.2.5.1 indicates that if the maximum ceiling temperature does not exceed 100° 
Ordinary sprinklers are to be used.

 

I know this is a gray area we take advantage of to ensure our fitters don’t 
have to look at what they’re installing, but is it technically in compliance 
with code?

 

 

B.J. Newlin

Service Sales

Aegis Fire Protection LLC.

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten. “--Benjamin Franklin

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of ron fletcher
Sent: Thursday, November 8, 2018 2:56 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Sprinklers next to Diffusers

 

Why not use intermediate temp heads everywhere? Then diffuser proximity won't 
matter.

 

Ron F

 

On Thu, Nov 8, 2018, 1:57 PM Kyle.Montgomery <kmontgom...@aerofire.com 
<mailto:kmontgom...@aerofire.com> > wrote:

What Steve said.

 

Generally, my experience has been that if they have a heat pump, max outlet 
temperature will be less than 100 degrees. But if they have a furnace, there is 
a good chance it will be higher. Mechanical designer/contractor should be able 
to answer the question.

 

-Kyle M

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> ] On Behalf Of Steve 
Leyton
Sent: Thursday, November 8, 2018 12:20 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: [EXTERNAL] Re: Sprinklers next to Diffusers

 

Higher than the ambient temp rating of the subject sprinkler.

 

 

 

Steve Leyton  

 

(Sent from my phone; please excuse typos and voice text corruptions.)

 

 

 

-------- Original message --------

From: Jerry Van Kolken <jvankol...@mfpc.us <mailto:jvankol...@mfpc.us> > 

Date: 11/8/18 8:47 PM (GMT+03:00) 

To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org>  

Subject: Sprinklers next to Diffusers 

 

NFPA 13-2016 Table 8.3.2.5 (c)

 

Reads 

 

Side of ceiling- or wall-mounted hot air diffuser  Minimum Distance from Edge 
of Source to Ordinary-Temperature Sprinkler  - 24” 

 

What is the temp of “Hot Air”?

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org