Ah. Missed the original question.

On Mon, Dec 3, 2018 at 11:36 AM Mike B Morey <[email protected]> wrote:

> His question (and my answer) were regarding FM Datasheet 3-26.
> ------------------------------
>
> *Mike Morey*
> *CFPS 3229 • NICET S.E.T. 123677*
> *Project Manager* • Fire Protection Group
> * Shambaugh & Son, LP **an EMCOR Company*
> 7614 Opportunity Drive • Fort Wayne, IN • 46825
> *direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
> * email *[email protected]
>
>
>
>
>
>
>
> From:        Ron Greenman <[email protected]>
> To:        [email protected]
> Date:        12/03/2018 12:02 PM
> Subject:        Re: Interior Loading Docks
> Sent by:        "Sprinklerforum" <
> [email protected]>
> ------------------------------
>
>
>
> BE ADVISED - This email originated outside EMCOR.
>
>
> Why edition are yo looking at. Chapter 2 is referenced publications in all
> recent editions and chapter 21.1 (I was speculating on a typo) ends the .1
> section at 21.1.9 in the 2016 edition. I'm at home and all my earlier
> editions are at the office.
>
> This is what the 2016 edition has to say about EC sprinklers in chapter 21:
> *Chapter 21 Alternative Sprinkler System Designs for*
> *Chapters 12 Through 20*
>
> *21.5.3 Extended Coverage Spacing Sprinklers.*
> *21.5.3.1*Sprinklers having extended coverage areas requir-
> ing up to 10 sprinklers to be included in the hydraulic calcu-
> lation shall be installed in accordance with the obstruction
> criteria described in 8.8.5.1, 8.12.5.2, and 8.12.5.3, unless
> large-scale fire testing is conducted with a representative ob-
> struction below the sprinkler that demonstrates equivalent
> performance.
> *21.5.3.2*CMDA and CMSA sprinklers having extended cover-
> age areas requiring more than 10 sprinklers in the design area
> shall be installed in accordance with the obstructions to sprin-
> kler discharge criteria described in 8.11.5 and 8.8.5.1.
>
> *21.5.3.2.1*ESFR sprinklers having extended coverage areas
> requiring more than 10 sprinklers in the design area shall be
> installed in accordance with the obstructions to sprinkler dis-
> charge criteria described in 8.12.5.2 and 8.12.5.3.
> *21.5.3.2.2*Other obstruction criteria shall be acceptable if
> large-scale fire testing is conducted with a representative ob-
> struction below the sprinkler that demonstrates equivalent
> performance.
> *21.5.3.2.3*When utilizing upright CMSA, CMDA, or ESFR
> sprinklers, any continuous obstruction 4 in. (100 mm) or less
> shall be permitted to be ignored.
>
>
> Ron Greenman
>
> *[email protected]* <[email protected]>
>
> 253.576.9700
>
> The Universe is monstrously indifferent to the presence of man. -Werner
> Herzog, screenwriter, film director, author, actor and opera
> director (1942-)
>
>
> On Mon, Dec 3, 2018 at 5:28 AM Mike B Morey <*[email protected]*
> <[email protected]>> wrote:
> 2.1.1.10.1 specifically states extended coverage heads are only allowed in
> wet pipe systems.
>
>
> ------------------------------
>
> * Mike Morey*
> * CFPS 3229 • NICET S.E.T. 123677*
> * Project Manager* • Fire Protection Group
> * Shambaugh & Son, LP **an EMCOR Company*
> 7614 Opportunity Drive • Fort Wayne, IN • 46825
> * direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
> * email **[email protected]* <[email protected]>
>
>
>
>
>
>
>
> From:        JD Gamble <*[email protected]*
> <[email protected]>>
> To:        "*[email protected]*
> <[email protected]>" <
> *[email protected]*
> <[email protected]>>
> Date:        11/30/2018 04:31 PM
> Subject:        Interior Loading Docks
> Sent by:        "Sprinklerforum" <
> *[email protected]*
> <[email protected]>>
> ------------------------------
>
>
>
> BE ADVISED - This email originated outside EMCOR.
>
> I have a project with an interior truck loading bay in a light
> manufacturing facility.  Looking at using FM3-26 as the basis of design,
> which allocates the design density as .3/3500 for a dry system at HC-3.
>
> Am I reading right that I and limited to using standard coverage
> sprinklers only on a dry system? (Referencing Table 2)
>
>
>
> Get *Outlook for iOS*
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__aka.ms_o0ukef&d=DwMFAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=tNMcU7aVpVRha9JcMzs39hOuLdm2QoM9scTpI3I31xE&s=mTz0h3wiqwf7mow0Q26eCn501DRspcQ4p8keH8M2HQk&e=>
> _______________________________________________
> Sprinklerforum mailing list
> *[email protected]*
> <[email protected]>
>
> *https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=tNMcU7aVpVRha9JcMzs39hOuLdm2QoM9scTpI3I31xE&s=rrzwRpv8Si_IKjX2y_kEHeVLzrG7Ibldya6MUbVDgGY&e=*
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=tNMcU7aVpVRha9JcMzs39hOuLdm2QoM9scTpI3I31xE&s=rrzwRpv8Si_IKjX2y_kEHeVLzrG7Ibldya6MUbVDgGY&e=>
>
> This message is for the named person's use only. It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission. If
> you receive this message in error, please immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender. You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
> _______________________________________________
> Sprinklerforum mailing list
> *[email protected]*
> <[email protected]>
>
> *http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org*
> <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=he_eRhPhSxdj-usBQYM9-Q4OG8mKEVnIedKHL55IFYo&s=6COyQ4_SfqlG4wcq_wzenNr1AGq5Aovl3TmItpgYJr4&e=>*[attachment
> "noname" deleted by Mike B Morey/Shambaugh/EMCORGROUP] [attachment "noname"
> deleted by Mike B Morey/Shambaugh/EMCORGROUP] *
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=he_eRhPhSxdj-usBQYM9-Q4OG8mKEVnIedKHL55IFYo&s=6COyQ4_SfqlG4wcq_wzenNr1AGq5Aovl3TmItpgYJr4&e=
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> --
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to