Due to the change of occupancy the sprinkler system should match the
requirements of the new occupancy.

If quick response sprinklers are required for code compliance then they need
to be changed.





Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell







From: Sprinklerforum [mailto:[email protected]]
On Behalf Of John Irwin
Sent: Thursday, January 03, 2019 4:29 PM
To: [email protected]
Subject: Indoor Trampoline Park



Some versions of this discussion have come up over the past weeks. We’re
having a bit of an issue with an AHJ in converting a Sports Authority to in
indoor park. Originally we submitted as Light Hazard because it’s an
assembly occupancy. I didn’t necessarily agree with this but … anyway …



The AHJ then wanted all sprinklers changed because they are 286° sprinklers
and thus, not permitted in LH.



So I spoke to said AHJ and told him I really felt this should be at least an
OH occupancy anyway, because of the miscellaneous foam padding and plastics.
He agreed (of course verbally and not in writing). We made those changes and
a couple more he asked for and thought we were good to go.



Today, we received this notice:





Mr. Irwin,

Just a follow up to our phone call earlier.

Thank you for speaking with me earlier.

The existing Fire Sprinkler System was designed and engineered to protect a
specific hazard for the previous occupancy.

There has been concerns about the potential need for reengineering since the
beginning of this project.

Sprinkler Systems in Assemblies are intended for life safety and are
designed as light hazard occupancies with fast activation per NFPA 13.

The proposed Fire Alarm System does not include smoke protection and will be
primarily activated by the Sprinkler System.

The proposed plans are for ordinary group II hazard with high temperature,
standard response sprinklers.

A delay in activation of the Fire Sprinkler and Fire Alarm Systems, may
result in an adverse effect on life safety.

This delay may increase the amount of fire damage.

Additionally this delay and the proposed 8K sprinklers may increase the
amount of water damage.

Please provide a signed and sealed letter from the Engineer of Record
documenting the effects the proposed fire protection systems will have on
occupant notification, occupant evacuation, life safety, and property
conservation.



Options:



*       The Engineer’s letter adequately documents that life safety will not
be adversely effected.
*       The Engineer’s letter indicates a change in hazard classification
and sprinklers.
*       The Engineer’s letter indicates the addition of full smoke
protection to the fire alarm system.



Please be advised that Engineer’s letter along with the most recent revision
will be will be sent out for a third party review by a Fire Protection
Engineer.



Thank you,



I’d especially like to know what Matt and Pete think about this. The
question is, is it always ok to over protect an occupancy? Assuming this is
a LH assembly (which I don’t agree it is) can I protect per OH if I want to?



As a sprinkler contractor, do I have to take alarm activation in to
consideration at all?



How would you proceed with this?







John Irwin

Quick Response Fire Protection

[email protected]

CELL – 727-282-9243





---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to