I recently did a system upgrade of an OH pipe schedule system with 130
SF/head..

Good water supply and  a low storage height made it work easily.

Back then only hazardous liquids were designed to extra hazard pipe schedule
and K8 - 90 SF/head.

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Spencer Tomlinson
Sent: Wednesday, January 16, 2019 5:26 PM
To: [email protected]
Subject: Storage Occupancy - Pipe Schedule

 

All - I have a unique situation, unique to me anyway.  Pipe schedule storage
occupancy installed per the 1969 edition of NFPA 13.  It looks to me that
NFPA 231 didn't come out until 1972, meaning storage would have fallen under
what I assume was one of the extra hazard curves in NFPA 13 in 1969 (unless
I'm missing something or misinterpreting this, I have a copy of neither but
would greatly appreciate anyone who may have access sharing).  NFPA 13, 2016
edition will allow for the use of a pipe schedule extension of an existing
"extra hazard" system per 11.2.2.3(2).

 

I have hydraulically calculated the extension, and it results in huge
piping.  Which is fine, but there may be an argument by others that pipe
schedule would be allowed.

 

Now, I know that it is certainly not the best approach - but that aside -
has anyone run into an instance such as this where the pipe schedule
extension has been allowed/approved?

 

Thanks to all in advance.

 

Spencer Tomlinson

Principal, PE

 

red logo

Ph:  316-202-6412

Fax: 316-202-2346

Cell: 620-955-7293

www.tomlinsonfire.com <http://www.tomlinsonfire.com/> 

 



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to