I’ve seen this condition happen pretty regularly. I’m not aware of anything 
prohibiting it. I suppose you are concerned about the potential impact to 
sprinkler activation?

-Kyle M

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jamie Seidl
Sent: Monday, February 4, 2019 1:35 PM
To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Subject: Re: [EXTERNAL] ESFR & exhaust fans

The curb is above our branch lines, and the louvers are in the roof 
penetration. I should have clarified they are roof top exhaust fans.

On Mon, Feb 4, 2019 at 3:27 PM Prahl, Craig/GVL 
<craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com>> wrote:
Can you clarify the location of the curb, it is ABOVE your sprinkler or below 
your sprinkler?

Are the louvers in the exterior wall, high near the roof line?

Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.jacobs.com_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=B49KR0wZd4K8V2hglyFZU7EuTNrPIyOyoA-l6vbazqQ&s=Vb2WdqBIzVtzTuOzS6_OFMssk7sBnDeXY93sk2xMCb0&e=>

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Jamie Seidl
Sent: Monday, February 04, 2019 2:59 PM
To: Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [EXTERNAL] ESFR & exhaust fans

Hello Forumites,
I have an issue that has come up with respect to exhaust fans in a warehouse we 
are completing.  Initially, the locations were coordinated with the mechanical 
contractor, and our branchline locations, however, his plans were never 
updated. The exhaust fan curb and gutter roof penetration is located directly 
below our sprinkler.  The exhaust fan itself is located on the roof, and the 
louvers are flush with the roof deck on the interior.  There is no obstruction 
that is created, but I can't find anything in NFPA 13 that would address this 
issue.
Is this an acceptable situation?
Thanks for your help,
Jamie Seidl

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=B49KR0wZd4K8V2hglyFZU7EuTNrPIyOyoA-l6vbazqQ&s=67-8THybo91RwXea-IcEnVlmuhaiPOSdBwe3rrIH-fY&e=>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to