An aquifer is not considered a raw water source so wouldn't a well be similar?  
Is it considered potable?

NFPA 13 says that water sources that are closed or protected from direct 
contact with the environment should not be considered raw.  2019 A.3.3.174

The biggest challenges with wells is the lack of consistency of the water 
supply and the unknown available volume.

For something that required an ESFR system, I'd be very wary of a well as my 
primary water supply.  Use the wells to fill a tank so you can be assured of 
having water when you need it.

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum <[email protected]> On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Monday, February 04, 2019 5:00 PM
To: [email protected]
Subject: [EXTERNAL] Well Water - Raw or non-raw

Would a well be considered a raw or non-raw water source?  We have a project 
close by a river that will need a water supply other than the municipal supply 
(it is not sufficient).  The system will be an ESFR system, so if the well is 
considered raw, then each sprinkler would need return bends and that is going 
to be prohibitive.

[MFP_logo_F]<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=en-j0JCuhvFLaKy5mroM8Mu9Yylvt87cyFq2goMvdPc&s=EHEQINbEEfkIno37Dqc1LVMXtAS3dL_f87LQ7Gwvhzo&e=>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=en-j0JCuhvFLaKy5mroM8Mu9Yylvt87cyFq2goMvdPc&s=tql7BChOqHYDpzfDIsR6fVsY8bwY-AXxDKgT3YCDUdc&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=en-j0JCuhvFLaKy5mroM8Mu9Yylvt87cyFq2goMvdPc&s=Aw7O7LCyfnXL9NJ5HcC3Ex9Dmkm0EC-3ai5X24Dh-iY&e=>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to